Problem:
Charging > 20 amps on my 280Ah battery sometimes causes cell1 (negative) and often cell16 (positive) to spike over voltage.
Patterns Noticed:
Current settings: (see attached for screen captures) These are mainly stock
The system is currently in this state and I have not tried to restart it yet.
Charging > 20 amps on my 280Ah battery sometimes causes cell1 (negative) and often cell16 (positive) to spike over voltage.
Patterns Noticed:
- When first charging every cell ramped up in voltage at the same time. It wasn't until voltages neared 97% SoC that cell 1 would be over active. The SMA SI was pushing 5.2kW into the batteries and everything seemed fine.
- (need to confirm) Removing AC IN and discharging to 50% then allowing for AC IN is when the problem presents itself last.
- (need to confirm) Restarting whole system with AC IN enabled near start up removes problem
- Cell1 / 16 have highest bypass .. all other cells 0
- When I noticed the problem, and adjusted the amps down, I had to go down to about 10 to have the problem stop, then I ramped back up but couldn't go beyond 20
- swap out k9 or another one I have lying around (I have a couple waiting for future packs)
- move cells1 and 16 to 2 and 15 to see if problem follows them
- Confirm patterns above which I have noticed at least twice so far
- Check voltage at cell one to confirm reading in batrium and adjust batrium as required
Current settings: (see attached for screen captures) These are mainly stock
The system is currently in this state and I have not tried to restart it yet.