Hmm… wonder if it’s because I was off-grid from the get-go? Perhaps the timer only counts time on the grid-tie options?You definitely have something exceptional going on there. My country settings are all locked and require grid guard.
Thanks!You'll need to change it from the standard to "Island Mode".
Sure. Yes, connect to the inverter via https://your-inverters-ip (wifi or ethernet), and sign in as the installer, as you said. Visit "Device Parameters", click "Edit Parameters". Under "Grid Monitoring", find "Set country standard" dropdown. Choose "SMA Island mode 60 Hz", click "Save All" button on top. Maybe it's because I didn't go through the installation assistant, or maybe it's normal? But I've got 100+ days of operating time, 5+MWh of production, and that option is still there. I actually just changed it, just to confirm that I could, and it did "take", no Grid Guard Code required.
Thanks for the responseOne thing I've heard is that SI may do a poor job of estimating SoC (although it is said to be good at maintaining lead-acid.)
I assume you're using lithium. What battery or BMS, and is there communication?
Current Connected has SOK batteries working closed-loop with SI, think he said some issue with bottom 20% of SoC.
Other members use REC, closed loop.
Some members use open loop.
How do you know battery SoC, is that BMS?
Are you using SI open-loop, with VRLA settings?
If so, could be battery voltage isn't down to SI's "float" setting yet.
I think 48V nominal VRLA settings can't match LiFePO4 voltages. A different nominal does, it may be 46V nominal VRLA.
I’m keen to know more about the lorenz switch. I’ve been searching for something that will only allow a load to run when enough PV generation is available.Time will tell, this is for a school so the reality is the batteries get used very little (nobody is there at night), well pumps have a Lorenz switch so they can only run when the sun is producing enough energy to run them. Have water storage on the roof if needed. Trophy did not want the equalize funcion so voltage is set the same as float, and they gave me the float voltage they wanted....
Hey just to let you know the Lorentz sensor is working perfectly. I have it connected directly to the vfd drives on our well pumps, then adjusted it so they only can come on if the solar is producing more than what they consume. We may eventually hook more loads but for now we have more than enough power for everything-- it is mostly protection in case somebody leaves the water on we don't have 2 well pumps running all nightI’m keen to know more about the lorenz switch. I’ve been searching for something that will only allow a load to run when enough PV generation is available.
Cheers!
Could you please send me a link to what you are using?Hey just to let you know the Lorentz sensor is working perfectly. I have it connected directly to the vfd drives on our well pumps, then adjusted it so they only can come on if the solar is producing more than what they consume. We may eventually hook more loads but for now we have more than enough power for everything-- it is mostly protection in case somebody leaves the water on we don't have 2 well pumps running all night