the motor is part of the valve body
Uh oh. Getting an error F09 from the LV6548. Checked the manual and it says "bus soft start failed" and the fix is to return it to a repair facility...
So far all I've tried is to reset it, and to disconnect battery power and disconnect grid power for 10 min and turn it back on. Still throwing F09.
No electrical smells, but I was testing the AC charging system, charging at 100a (is rated for 120a) and it threw a F02 for over temp. Then a few minutes later the F02 cleared and it threw F09.Do you smell electrical burning smells in the compartment?
Failure is odd as following your thread you have yet to really get it loaded up close to 100%
did you take a voltage reading of your batteryGood news. I was able to disconnect the all power (Grid, PV and battery) and i turned them back on one at a time. First PV only, and it worked great. I even ran 2 ACs on solar power alone! It has enough surge to simultaneously run 1 AC, while it starts another one! Incredible!
Then I flipped on The grid ac input, and all is still well. Im guessing it's something wrong with the battery side.
A side note, I can't connect to the BMS in my battery, I hope that's not my problem... but im going to pull the lid off the battery and check it out
Voltage shows 53.3v.did you take a voltage reading of your battery
Unfortunately no, I wish it was that easy. That is the battery input and it has a polished finish. It is just the reflection of the fan directly above it.
I just watched a solar panel review by a guy who installs them. He rates Sunpower as the best panel over LG, Tesla, and Panasonic.I'm starting to think... I have 36 panels total (12 on the roof, 12 on the ground, and 12 im not using). And I'm wondering if I can somehow wire in more of these panels to get full usage of this LV6548. I have a max 8000 watt input, and I rarely see over 4000 watts and have never seen over 4200 watts.
How can I do this safely?
Edit: im doing the math now, my current array is 205VOC (measure with a multimeter), which means each panel is 34.16v, and 7 panels would be 239v, which is less than 250v max. I know it's dangerous to get close to that limit, but its doing nothing but getting hotter here, and soon we will be seeing 80-85* at 3 am. It gets very hot here, so I think I'll be safe until later in the year.
Also, I see im never pulling more than 14-14.5amps continously, and after talking with Ian, these units can safely be overpanneled to 23a (instead of the advertised 18a max). Well, 14.5a/2 (because of the 2 parallel strings = 7.25a each string, and 7.25x3 = 21.75a.
So with this little math I've done, I have proved i can safely hook up a 7s3p system and use 21 of the 24 panels total? To check my math and also not go over the 4000watt limit per PV input, 21 panels x 166 watts (which is what I'm currently averaging per panel) = 3486 watts. So as long as I don't get over 190 watts per panel (which so far has been unattainable), then im good.
I just watched a solar panel review by a guy who installs them. He rates Sunpower as the best panel over LG, Tesla, and Panasonic.
Good tip. Thanks. I heard Tesla uses Panasonic and Qcell. Is that not correct?The local installer guy around here says Tesla are by far the best as a nicely engineered solution. After that he says LG, Panasonic are really good and he considers them tier-2. Then the next level is REC alone in tier-3. Everything else is a step down from that point.
For REC he said you need to spend to get the high power versions as not only are they more efficient but also put together with more care and attention.
Also he says doesn't matter the vendor - test EVERY panel before it gets to the roof as they all have plenty of DOA's and they tend to come in batches.
Good tip. Thanks. I heard Tesla uses Panasonic and Qcell. Is that not correct?