SI multi-function relay has option "AutoGn Automatic generator request The generator is automatically activated due to set
criteria (see Section 14.1.5 "Automatic Generator
Operation", page 123)."
You could use that to signal you when manual generator needs to be started.
I guess it could provide an additional load-shedding control as well.
I would hope everything require for care and feeding of SI could be found by RTFM.
"Value for parameter "234.03 GnCurNom"
A sensible value for parameter "234.03 GnCurNom" is approximately 80% of the maximum
generator current for each line conductor."
"If the parameter "234.15 GnCtlMod" is set to CurFrq, the generator is also limited at frequencies
lower than the nominal frequency (parameter "234.04 GnFrqNom"). This function can be used if the
full generator power is not always available and you want to prevent the generator from being
overloaded. The default setting is only intended to control the nominal generator current.
If the current set using the parameter "234.03 GnCurNom" is not sufficient for powering the loads,
the battery provides support ("real generator support").
The Sunny Island provides all the required reactive power."
So that one appears to be per SI, whether single-phase 4p configuration or split-phase 2p2s.
I remember setting larger values than 56A for grid current, up to 112A with two SI in parallel.
Could be that is due to quick-start menu, where we apparently type in the total current. But the parameters accessed in other menus are per inverter?
"
GenGrid:
– Maximum generator current (0 A - 224 A), default setting: "16 A"
– Generator interface (Manual, GenMan, Autostart), default setting: "Autostart"
– Maximum grid current (0 A - 224 A), default setting: "16 A"
"
Except during quick-start, it seems.