SilverbackMP
Solar Addict
- Joined
- Apr 4, 2022
- Messages
- 928
Fairly certain my woes are cured. I think it was mostly the generator sensitivity but I also think the battery size was wrong and it’s right now.
Yes!!Fairly certain my woes are cured. I think it was mostly the generator sensitivity but I also think the battery size was wrong and it’s right now.
It’s set at 240 amps (battery charge) right now charging around 9.5 kw. I didn’t realize it, but my electrician had installed a 50 A main breaker in the generator sub panel as temp measure as he didn’t have another 125 A and #1 wire on hand. As soon as I got right in the Sunny Islands, it started firing off that breaker. It’s been running an hour straight like this. I would give odds it will work at higher amps when we get the main generator breaker and wire replaced. Final breakers will be 125 A from the generator (@240) and 70s for each of the SIs (@120v).Yes!!
That's bloody exciting. Please keep us updated. I want to know how many minutes or hours you are able to run without it shutting off and what max amp rate it'll take. Thanks
Cool. Glad it's working because I know a couple of people had mentioned trouble with the sunny island synching to the generator.It’s set at 240 amps (battery charge) right now charging around 9.5 kw. I didn’t realize it, but my electrician had installed a 50 A main breaker in the generator sub panel as temp measure as he didn’t have another 125 A and #1 wire on hand. As soon as I got right in the Sunny Islands, it started firing off that breaker. It’s been running an hour straight like this. I would give odds it will work at higher amps when we get the main generator breaker and wire replaced. Final breakers will be 125 A from the generator (@240) and 70s for each of the SIs (@120v).
Ingersoll Rand 30KW powered by a Cummins 4BT. Bought used six or seven years ago.Cool. Glad it's working because I know a couple of people had mentioned trouble with the sunny island synching to the generator.
What type of generator do you have if you don't mind my asking?
I don’t see anything that looks applicable.Does REC BMS have separate limits for continuous and surge, with time limit for surge?
This is from the REC manual from the start of the threadMy question is…should this be raised to 112A per current device to allow for max start up surge per SI stated capability?
I can work around most surge issues…my HVAC (part of it anyway) are inverter mini splits. Most of my wood working stuff (3 HP sawstop, Harvey 2 HP G700 Dust processor, etc has soft start or on board VFD).This is from the REC manual from the start of the thread
Maximum charging/discharging current per inverter device 90/100 A
So I would not enter 112A to cover the inrush as that then leaves it open for 112A to occur by accident at another point and damage the REC.
If only the inrush is the issue then I would keep the 60A and use resistors or loads with a 3 way switch to cover the inrush by limiting the amps to below 60A.
As the 60A is only an issue during the inrush then fix the inrush instead of leaving a setting above what the REC wants.
Five 48v batteries so 5 REC's at 60A each is 14kw or 18HP
At 90A is 21kw or 27HP
Even if you reduce those figures to cover what you have on in the rest of the house I don't see a problem unless you have a few other Silverbacks to operate the machines all at the same time.
I doubt they have transformers…judging from the physical size….which are about the size of new school stick welders.Does plasma cutter have transformer front end or rectifier/capacitor feeding inverter?
Transformers have inrush (highly variable, has to do with magnetization of core by AC phases), and capacitors have inrush.
So long as they can be powered on without load (unlike compressor motor), could power up through something resistive, such as an Antherm thermistor. The thermistor is automatic, and runs HOT to maintain low resistance.
A series resistor with bypass switch could precharge. That could even be a length of wire, if the resistance is sufficient. For instance a roll of Romex, current goes out through the black, connect to white, back through that. No inductance that way, just wire resistance.
Want to avoid "brownout" with excessive resistance/time, in case SMPS in the device can't handle that.
That’s a beautyIngersoll Rand 30KW powered by a Cummins 4BT. Bought used six or seven years ago.