I watch them ramp up slowly. That is the MPPT drawing PV voltage down.
But a load dump happens instantly. Question is what island grid voltage does, and how GT PV responds. I think of GT PV inverter as SMPS for current, with current being a sine wave proportional to voltage. Or maybe proportional to a software PLL following grid voltage.
I'll try the motor-generator, set to run no-load at a frequency which will decrease GT PV output to zero watts but not disconnect. SB off-grid default setting, 62 Hz < no-load frequency < 64 Hz. For a
UL-1741-SA inverter, not clear that it is supposed to remain connected indefinitely when above 61 Hz, the 0W point.
Playing with TriPower, I ended up in a mode where frequency-watts ramps down from 100% at 60 Hz to 0% at 60.5 Hz.
You would want PV not battery to keep motor-generator turning no-load, but don't want to overcharge either. I think this system would be most optimum for hydro plant, with water flow adjusted to regulate frequency. Typical micro hydro would be Pelton wheel with constant flow, DC output into charge controller. It will either go to 2x RPM no-load, or else need a dump load.
But a load dump happens instantly. Question is what island grid voltage does, and how GT PV responds. I think of GT PV inverter as SMPS for current, with current being a sine wave proportional to voltage. Or maybe proportional to a software PLL following grid voltage.
I'll try the motor-generator, set to run no-load at a frequency which will decrease GT PV output to zero watts but not disconnect. SB off-grid default setting, 62 Hz < no-load frequency < 64 Hz. For a
UL-1741-SA inverter, not clear that it is supposed to remain connected indefinitely when above 61 Hz, the 0W point.
Playing with TriPower, I ended up in a mode where frequency-watts ramps down from 100% at 60 Hz to 0% at 60.5 Hz.
You would want PV not battery to keep motor-generator turning no-load, but don't want to overcharge either. I think this system would be most optimum for hydro plant, with water flow adjusted to regulate frequency. Typical micro hydro would be Pelton wheel with constant flow, DC output into charge controller. It will either go to 2x RPM no-load, or else need a dump load.