So I could just get a cheapo monitor like this?
Nope. It looks like it bases the state of charge on voltage, not current in/out. Also, there is this in the description:
Note: it cannot be used for Lithium Iron Phosphate batteries
So I could just get a cheapo monitor like this?
Note: it cannot be used for Lithium Iron Phosphate batteries
My bad, hadn't read the description.Nope. It looks like it bases the state of charge on voltage, not current in/out. Also, there is this in the description:
Lots of options. The % and graphic may not work that accurately.
Here is a 3 decimal meter for $11, your call.
https://www.amazon.com/DROK-Voltmeter-Mounting-0-33-000V-Voltage/dp/B00CJRE1PM
The MultiPlus is an inverter, charger, and transfer switch combined into one unit. This lets you connect AC power in which can be used to charge the battery and/or provide AC out. It also allows you to get AC out just from the battery. Such a unit is much simpler than buying a separate inverter, separate charger, and separate transfer switch and wiring them together. I would definitely consider the MultiPlus over the separate devices.
BTW - unrelated to that decision, do keep in mind that both the Phoenix 12/500 and the MultiPlus 12/500 are rated at 500VA, not 500W. They are both actually 430W. Just something to consider based on your actual wattage needs. The next size up is the 800VA models which are 700W.
Thanks.The Multiplus 12/500 has an efficiency of 90% at 12 volts. You wouldn't want your LiFePO4 cutoff at 9.3 volts. Most of its life will be spent above 12.0 volts. I used 430 watts continuous since that's what the 12/500 is actually rated for. Even with those revised numbers, 8 gauge wire is a bit skimpy.
Oh right, I didn't think about the fact that the specs aren't specifically for LiFePO. Are there other settings I need to worry about?430W / 12V / 90% = 40A. 6AWG and a 50A fuse would be right.
300W / 12V / 90% = 28A. 8AWG and a 35A or 40A fuse would be right.
Remember that for LiFePO₄ batteries, 10.0V is 0% SOC. 12.0V is just under 10%. Don't let the batteries get below 12.0V. Be sure you set the inverter's LVD to 12.0V or higher.