Well, my call with the tech specialist goes nowhere. I need a senior Engineer to speak with. And please listen to that phone call. I've been more help to SS than they have to me... Really. Cmon SS.
Anyway, I took a closer look at the log data and something is definitely not right.
In the BAR graphing menu it, shows the total energy drawn from the battery, but in the spreadsheet log and line graph, it does not show battery discharging.
In AC Charging mode, 1st priority is energy from grid AND no discharging from battery, period.
The Spreadsheet log is NOT completely correct.
It's obvious that if there was exporting to grid and with my sub panel constant load running; the energy has to come from the battery at 4AM.
My BMS confirms a draw of 600-1100W during the exporting period, the Bar charts show Battery discharging, yet nowhere in the spreadsheet logs or the line graph does it show.
So my question is where are the data being polled from. Again, it's very obvious the spreadsheet data is wrong in a lot of the columns.
Look closely at the spreadsheet info. I've hi-lited the important columns for the coders to really take a look at.
I can for sure say I still have a constant inverter load of 200-400W. This is because I have network gear and surveillance systems running 24/7 and there is no reports of power issues.
My only objective is to make this 18Kpv work like it is described in the white sheet or manual ( hopefully both).
So man, let me speak to someone that can make the correct changes in the code or tell us, it can not work the way We all thought it would.
Anyway, I took a closer look at the log data and something is definitely not right.
In the BAR graphing menu it, shows the total energy drawn from the battery, but in the spreadsheet log and line graph, it does not show battery discharging.
In AC Charging mode, 1st priority is energy from grid AND no discharging from battery, period.
The Spreadsheet log is NOT completely correct.
It's obvious that if there was exporting to grid and with my sub panel constant load running; the energy has to come from the battery at 4AM.
My BMS confirms a draw of 600-1100W during the exporting period, the Bar charts show Battery discharging, yet nowhere in the spreadsheet logs or the line graph does it show.
So my question is where are the data being polled from. Again, it's very obvious the spreadsheet data is wrong in a lot of the columns.
Look closely at the spreadsheet info. I've hi-lited the important columns for the coders to really take a look at.
I can for sure say I still have a constant inverter load of 200-400W. This is because I have network gear and surveillance systems running 24/7 and there is no reports of power issues.
My only objective is to make this 18Kpv work like it is described in the white sheet or manual ( hopefully both).
So man, let me speak to someone that can make the correct changes in the code or tell us, it can not work the way We all thought it would.