My system is (or was, I dismantled it):
2 100w HQST solar panels in series
50' solar cables
victron MPPT 100 | 30 SCC
2' 12 gauge solid conductor wires, positive fused with 40 amp automotive spade-type fuse
2 battleborn 12v 100 Ah batteries wired in parallel
6' 2 gauge 130 degrees C stranded wires
Harbor Freight Item #63432 Jupiter 1500 Watt Modified Sine Wave Inverter
I was using the system off grid to run 2 florescent shop lights (total combined load 115 watts), charge a laptop, run a 1000 watt pressure cooker, run a small fan. All was working fine for months. Then I started running the shop lights for more hours. I'd still make sure that the system got into float mode every day. Looking at the victron connect app I was making about 1kWh a day. Then one day the lights started flickering and the inverter gave a low voltage alarm. That puzzled me because I hadn't been using a lot of power. I turned off the inverter and looked at the victron connect app and it said the battery bank was at 10.3v.
The next day the SCC went into float mode after about 1.5 hours. That puzzled me because I believe that 200w of solar panels in the morning couldn't possibly take a 200 Ah lithium battery bank from 10.3v to 13.6v in that amount of time. Later that day I tried running the shop lights again. Once again I got a low voltage alarm from the inverter in a very short amount of time. I turned off the inverter.
I suspected there was something wrong with that Harbor Freight inverter. So I disconnected the positive wire to it, but left the negative attached. I don't know why just the one wire, but that's what I did. I guess I figured that would be enough to keep the inverter from drawing any power.
I left the inverter off for a month. Each day the SCC would be in float mode. I used no power from the system. I figured the batteries were fully charged. After that month I used a multimeter and the batteries read 9.8v. More puzzlement. I disconnected the solar panels, then disconnected the batteries, and charged them each separately using a marine battery charger on the grid. Now I have 2 batteries holding steady at 13.37v.
I hooked one of the batteries up to the SCC just to look at the history in the victron connect app. It shows a month of data. It went from
14.6 v max, 10.0 v min on the first day with the v min going gradually down ferther each day over the 30 days. On the last day it showed 14.6 max 3.53 v min. I should have been checking what was going on, but life got in the way for a month there.
So now I'm lost. I guess maybe I should have disconnected the negative wire from the batteries to the inverter? I am thinking about hooking everything back up except for the inverter, then run a 12v compressor cooler for a while to see if I at least have the 12v side working properly. I would have to use that inverter to run a full load test on the battery bank, but I am fearful that the inverter has a short or some other malfunction. Since there's no fuse between it and the battery, I'm afraid to use it, given what's been going on.
My overall question is what is going on with this system? More specifically, is there a way to test if the inverter has a short that is draining the batteries? Why would the victron app indicate 3.53v and the multimeter indicate 9.8v?
I would be grateful for any assistance on how I can diagnose this and suggestions on how I could improve the safety and capability of my system. Like buying a quality pure sine wave inverter and a circuit breaker! I am in an remote area and there's very little I can buy locally. I do have a victron battery monitor bmv-712 smart that I could add into the system to get more useful information.
Thanks for reading all this if you made it this far! I hope I gave enough information for someone to help. I tried to search the forums for a similar discussion, but didn't find a good match in the search.
2 100w HQST solar panels in series
50' solar cables
victron MPPT 100 | 30 SCC
2' 12 gauge solid conductor wires, positive fused with 40 amp automotive spade-type fuse
2 battleborn 12v 100 Ah batteries wired in parallel
6' 2 gauge 130 degrees C stranded wires
Harbor Freight Item #63432 Jupiter 1500 Watt Modified Sine Wave Inverter
I was using the system off grid to run 2 florescent shop lights (total combined load 115 watts), charge a laptop, run a 1000 watt pressure cooker, run a small fan. All was working fine for months. Then I started running the shop lights for more hours. I'd still make sure that the system got into float mode every day. Looking at the victron connect app I was making about 1kWh a day. Then one day the lights started flickering and the inverter gave a low voltage alarm. That puzzled me because I hadn't been using a lot of power. I turned off the inverter and looked at the victron connect app and it said the battery bank was at 10.3v.
The next day the SCC went into float mode after about 1.5 hours. That puzzled me because I believe that 200w of solar panels in the morning couldn't possibly take a 200 Ah lithium battery bank from 10.3v to 13.6v in that amount of time. Later that day I tried running the shop lights again. Once again I got a low voltage alarm from the inverter in a very short amount of time. I turned off the inverter.
I suspected there was something wrong with that Harbor Freight inverter. So I disconnected the positive wire to it, but left the negative attached. I don't know why just the one wire, but that's what I did. I guess I figured that would be enough to keep the inverter from drawing any power.
I left the inverter off for a month. Each day the SCC would be in float mode. I used no power from the system. I figured the batteries were fully charged. After that month I used a multimeter and the batteries read 9.8v. More puzzlement. I disconnected the solar panels, then disconnected the batteries, and charged them each separately using a marine battery charger on the grid. Now I have 2 batteries holding steady at 13.37v.
I hooked one of the batteries up to the SCC just to look at the history in the victron connect app. It shows a month of data. It went from
14.6 v max, 10.0 v min on the first day with the v min going gradually down ferther each day over the 30 days. On the last day it showed 14.6 max 3.53 v min. I should have been checking what was going on, but life got in the way for a month there.
So now I'm lost. I guess maybe I should have disconnected the negative wire from the batteries to the inverter? I am thinking about hooking everything back up except for the inverter, then run a 12v compressor cooler for a while to see if I at least have the 12v side working properly. I would have to use that inverter to run a full load test on the battery bank, but I am fearful that the inverter has a short or some other malfunction. Since there's no fuse between it and the battery, I'm afraid to use it, given what's been going on.
My overall question is what is going on with this system? More specifically, is there a way to test if the inverter has a short that is draining the batteries? Why would the victron app indicate 3.53v and the multimeter indicate 9.8v?
I would be grateful for any assistance on how I can diagnose this and suggestions on how I could improve the safety and capability of my system. Like buying a quality pure sine wave inverter and a circuit breaker! I am in an remote area and there's very little I can buy locally. I do have a victron battery monitor bmv-712 smart that I could add into the system to get more useful information.
Thanks for reading all this if you made it this far! I hope I gave enough information for someone to help. I tried to search the forums for a similar discussion, but didn't find a good match in the search.