I have a totally off-grid system I've been building (NO utilities) in southern Colorado, USA.
The solar arrays are ground mounted (IronRidge) and about 125 linear feet from the garage where the inverters and batteries are located.
The garage is connected to my home with a 20 foot breezeway.
That said, I'm putting two grounding rods, 6 feet apart and connected to the two arrays by 4awg copper wires. Only PV wires run from the arrays to the garage inverters. In the garage the inverters will back feed their AC power to a Sub Panel with a separate breaker for each inverter (4 - EG4 120v). From their they will be combined into two legs (L1 and L2) along with the combing all neutral and all grounding wires into larger wires fed to the main house panel (single N, G, L1 & L2).
Since grounding rods are supposed to be attached by grounding wire to the "service entrance" panel, then in my Off-Grid case that would be the sub-panel, so I will feed two additional grounding rods from there, neutral/ground bonding will be done at the sub-panel. In a grid tied home, you would normally do the neutral/ground bond in the main house panel since that is where the service normally comes in.
I hope this helps.