- So a larger amp shunt will require larger gauge wire, correct? I was planning on using 2/0 to handle the 175a battery (which I never plan on getting close to using that amount of draw, probably no more than 50a), but with the numbers you provided, I would be looking at 4/0, correct?
- Selecting a 300a shunt far exceeds the calculated 226.1a, what type of protection does that actually provide? I would rather size wire based on battery sizing not shunt sizing. With that said, what is to stop me from getting a 500a shunt?
Wire size is dependent on amperes expected and distance. Use a voltage drop table or calculator such as this by Blue Sea. http://circuitwizard.bluesea.com/ You need a shunt that covers the amperes you expect to flow. Example from my life. Large bank. 2000W inverter. 150 dc amps when microwave on high. Sized for inrush from microwave. 300 amp fuse on positive. 2/0 cables. 500 amp shunt on negative. The amperes determine shunt size. The shunt doesn't add to the ampere load.
So back to the original question. What size shunt? I have a 250a main fuse run to main disconnect on the positive line. Why would I go way over size on shunt? You said you have a 500a shunt when only 400a is required, based on your 300a fuse x 1.33 = 399a. I know you aren't going to find a readily available shunt at 400a, but it just seems to me like it is pointless. Is it for lightning strike or something?
Just trying to learn. Thanks!
I think what he said was that when he expanded he was still going to keep the loads down.Not exactly. Victron BMS is a coulomb counter. OP stated he wants to have room for expansion.