Wait...
Peltier can achieve a COP of 3???
everything I have researched on peltier shows it as extremely inefficient...
Can you show the testing of this achievement?
Collected the following:
Count | Name | URL | usd |
---|
1 | 10pcs peltier element
TEC1-12715 |
| 50 |
2 | 1pcs thermal pad
12.8 W/mK, 85x45x0.5mm |
| 13 |
1 | 1pcs CPU heatsink
180W TDP 120mm |
| 65 |
1 | TekPower DC Bench Supply |
Buy TekPower TP1540E DC Adjustable Switching Power Supply 15V 40A Digital Display (TP1540E) with fast shipping and top-rated customer service. Once you know, you Newegg!
www.newegg.com
| was 190 |
1 | PC Fan 40x40x20mm |
| 15 |
1 | Non-Contact Infrared Thermometer |
| 30 |
Important Note:
Emissivity was not corrected for in this method. Need retesting with thermocouples to 16/24-bit ADC.
Procedure:
Connect positive of first element to negative of second element. Connect positive of second element to negative of third element.
Connect negative of first element to DC Bench Supply Negative. Connect positive of third element to DC Bench Supply Positive.
I set up a separate 12V supply for the PC fan. Any wall wart 12V should be fine.
Apply the thermal pads between the face of the heat sink and the successive peltier elements.
Sequence: heat sink -> pad -> peltier 1 -> pad -> peltier 2 -> pad -> peltier 3 -> air
Adjust Bench Supply Current up. Adjust Supply Voltage all way down. Turn on power supply with 3 series TEC1-12715 connected as described above. Confirm 0V 0A on supply.
Adjust voltage to 0.1V and wait 20 seconds for temperature to stabilize, then record heat pipe/fin temperature and cold face temperature using non-contact thermometer, ensuring to consistently and accurately point the IR sensor at the point of interest.
Repeat for 0.1, 0.2.. 1.0, 1.1, 1.2.. 2.0, 2.5, 3.0, 3.5, 4.0, 4.5, 5.0, 5.5, 6.0, 6.5, 7.0, 7.5 Volts. Note amps at each Volt Step. Wait for temperature to equalize at each stage. Ensure accurate aiming of thermometer. Try my best because the bench only has tenths precision.
Expectation: ~2.0V per module ( 3 modules in series * 2.0 per module = 6.0 V for string ) to be target for operation as per earlier post. Approximate voltage, need actual data sheet or better characterization.
Result: 2.0V per module resulted in heat pipe T=31.0°C and cold side T=-1.9°C for a dT = 32.9°C. 6.0V * 1.7A = ~10.2W.
Yes, deciWatts. 10 dW = 1W.
This legend should say power fit, not linear fit or polynomial fit. My bad. Will fix in an update.
Please forgive me for the poor formatting of the graphs, and likely an error of unit labels that I didn't notice. Used apple spreadsheet software which has limited control over the small details of graph format.
Curious what other people have to think about this. This represents a collection of random observations, likely with large oversights in design. Would kindly request respectful feedback that addresses these specific observations. Edited spreadsheet to show C not ambiguous "T".
After thinking a little about the topic of DC Regulation Efficiency, Another random observation..
Code:
> (3.0 V * 3 cells) / 5 layer
1.8 V / layer
> (3.4 V * 3 cells) / 5 layer
2.04 V / layer
> (3.65 V * 3 cells) / 5 layer
2.19 V / layer
TL;DR ran 10W @ 6 V through three peltier TEC1-12715 module in series and water condenses on the cold face when i breathe on it (quicker) or point a small fan at it (slower). hot side = 31°C, cold side = -1.9°C, dT = 32.9°C, RH ambient = 36%RH
Still, at the end of this post, I don't have a clear COP to give you
@Supervstech. Hopefully this is still fruitful for discussion. If anyone notices a flaw in the described methodology, please bring it up so that it can be addressed ?