12 460watt solar panels
51 voc
11.5 amps
Ran in 6s 2p
I need to stay under 450v for my LVX 6048. I have 2 of these units.
So my question is if I run 6 panels in series and then run 2 sets in parallel, then run 2 10awg wires to my set of LVX 6048's, then split those 2 wires into 4 wires at the PV disconnect, will it split the amps and volts back in half? Is it safe to do this?
My wire can handle the amps and volts I believe (correct me if I'm wrong). The LVX 6048 has a max 450v input. My problem is I'm trying save on wire because it is a 400ft run.
Hopefully this all makes sense.