Not long run at all but I have some 6awg PV wire I thought I use that6awg PV wire is way overkill unless it's a very long run. Most PV wire is 8-14awg with 10awg being the most common for the larger panels (60-72 cell 250W+).
Ok. 6awg wire and 75A fuse?60A to MPPT should be 1.25X wire rating. If it's 60A, and you're putting out 60A, it will blow. If wire rated for 60A, fuse @ 75A.
1/0 from MPPT to battery is complete overkill unless you have long wires.
Good question. 1 near positive terminal on inverter and 1 before DC>DC converter?Why does battery isolator only isolate from MPPT and not loads? Should isolate everything.
But if inverter draw max 6000W is not 300A fuse necessary?3000W/24V/.85 = 147A
I have no cables yet, but if that's the case, better to go with 2/0awg?Depending on temperature rating, 1/0 may only be good for 125A.
1/0awg @150A rating should be 200A fuse then?300A fuse should be 1.25X wire rating, and wire should be good for 147A or more.
Ok.6awg to 24V @25A fuse is overkill unless you have long wires.
Need fuse between DC-DC and fuse block.
That was my idea. I will have to check MPPT manual. Thanks for clarification.DC-DC may be more sensible off the battery unless you want to use the MPPT load ports for DC-DC cut-off, i.e., most MPPT load ports allow you to specify a minimum voltage at which the MPPT will cut power to the load ports to protect the battery. Ensure the load ports are rated for the needed current.
Not long run at all but I have some 6awg PV wire I thought I use that
Ok. 6awg wire and 75A fuse?
Good question. 1 near positive terminal on inverter and 1 before DC>DC converter?
But if inverter draw max 6000W is not 300A fuse necessary?
I have no cables yet, but if that's the case, better to go with 2/0awg?
1/0awg @150A rating should be 200A fuse then?
That was my idea. I will have to check MPPT manual. Thanks for clarification.
I'm a beginner to this so big thanks for helping out.
Other novice here.. can you provide a link to where you mocked up that diagram? ThanksHi!
I would greatly appriciate some feedback on this set-up. Should something be changed? Perhaps the DC>DC converter on battery instead?
View attachment 130983
Other novice here.. can you provide a link to where you mocked up that diagram? Thanks
Made with Adobe Photoshop.What software did you use to make that drawing?
Could you say as a general rule, bigger wire, bigger fuse/breaker?You can always use bigger wire. Just fuse/breaker accordingly.
I was wondering what those busbars was used for.Better to have a set of bus bars. The isolated would be between the battery and (+) bus bar with MPPT and Inverter attached to bus bar.
Ah, ok!You do not size for surge. You size for max continuous. Furthermore, if you were sizing for surge, 1/0 is not sufficient.
By meassuring on the positive battery wire?10-4 good buddy.
Lastly, assuming this is a DIY 8S 280Ah, ensure your BMS can handle the needed current. Also, I'm assuming you plan to use the BMS as a battery monitor for % charge and current. This is generally okay, but I would confirm the current measurement with a separate DC clamp ammeter before I trust it.
Will's site recommends a few good battery monitors if you want something that doesn't need a phone/tablet as well.
Could you say as a general rule, bigger wire, bigger fuse/breaker?
I was wondering what those busbars was used for.
By meassuring on the positive battery wire?