Ok so online it says I need 2/0 three stranded wire to run from my 3000w inverter to the breaker box. I am having a hard time finding such wire. Can anyone point me in the right direction?
Ok so online it says I need 2/0 three stranded wire
6 awg pure copper rated for 105 Celsius is fine for the dc side.So I have a growatt system that is all in one. I have 6 gauge wire between the batteries and the system is that not big enough? That is what was sold with the system and suggested by bigbattery.com
Probably absolute overkill.ok cool. and for the ac load is this good?
Yep absolute overkill.120VAC@60hz
I have the growatt SPF 3000TL LVM-ES inverter and it keeps triggering the breaker where I have the AC "IN" from the inverter to wall outlet (20 amp gfi)
Solar Enthusiast, you are the electrical man! That was the issue, the GFI I beleive from the grid was grounding itself out with the solars independent Ground and breaker box. Thanks allot, I was banging my head wondering. The house I live in has GFI's all over every circuit in the house, hard to find a circuit without GFI to try but in the end it worked perfectly as you suggested.Most likely has something to do with the GFI. Would try connecting to a non GFI circuit to test.
That is Unusual.Solar Enthusiast, you are the electrical man! That was the issue, the GFI I beleive from the grid was grounding itself out with the solars independent Ground and breaker box. Thanks allot, I was banging my head wondering. The house I live in has GFI's all over every circuit in the house, hard to find a circuit without GFI to try but in the end it worked perfectly as you suggested.
Most of the time any additional AC breaker boxes should use the main panels ground. Also ground should only be bonded to neutral in the main panel. If using a main panel as a subpanel, bonding strap-bar that bond neutral and ground should be removed.Correct on the 1 gfi per circuit, the previous owner of this house has GFIs all over the place. I had to install a new outlet directly from the grids main breaker box to get the AC IN working properly on the inverter. The grid breaker box has it's own grounding rod and is 100% independent from my PV, Inverters and additional breaker box. From the inverters I installed a breaker box complete with it's own grounding Rod out near my PV and combiner box. As you can see from the photo I'm pointing to the ground wire that runs directly from the PV breaker box to the ground 120' away with 8 way wire. The grounding Rod is 8' into the ground. The ground is shared with the Neutral on this breaker panel is it's a main breaker box and not a sub panel, everything look ok? Any advice is always appreciated. Thanks
I am not an electrician but neutral and ground should be bonded in one and only one place.Correct on the 1 gfi per circuit, the previous owner of this house has GFIs all over the place. I had to install a new outlet directly from the grids main breaker box to get the AC IN working properly on the inverter. The grid breaker box has it's own grounding rod and is 100% independent from my PV, Inverters and additional breaker box. From the inverters I installed a breaker box complete with it's own grounding Rod out near my PV and combiner box. As you can see from the photo I'm pointing to the ground wire that runs directly from the PV breaker box to the ground 120' away with 8 way wire. The grounding Rod is 8' into the ground. The ground is shared with the Neutral on this breaker panel is it's a main breaker box and not a sub panel, everything look ok? Any advice is always appreciated. Thanks