I hope I dont come off too big an idiot - I installed a 10.8kw system 10 years ago and will be removing that and upgrading. My goal is to have seamless transfer on power outages, upgrade watts, more techy inverters. Currently I have 400 amp service (200amp x2). My current inverters(schnieder 4.5kw) each have a 60amp breaker to power each of my 2 panels when power goes out(i have to flip a ton of breakers and its a pain). They feed the grid via 1x100amp breaker. I'm looking to overhaul everything and have been deciding between solark15k x 2 and EG4 18k x2 (leaning this way). I will be installing approx 60 Canadian solar 400amp panels evenly split between 2 inverters. Battery size 30-45kwh. Here are my questions:

1. I dont want to line side tap... Can I continue to use those 60amp breakers (1 in each panel, 1 per inverter) to feed my 200amp panels during outage?
2. Can I continue to feed the grid via 100amp breaker or will I need to do lets say ~60amp breaker per panel? 1 per inverter or how do you wire this?
3. Should I install a critical loads panel or just use 1 inverter per 200amp panel. The only time I could see overloading inverter would be if my heat pump was running during a cold day. Otherwise, its unlikely I would be pulling more than 60amps at any given time.

Any other advice? I think I have the install pretty well figured out other than how to feed my main breaker panels. It's sooooo much simpler than 10 years ago.
 
@neo2299 did you figure it out? What was your solution?
Yeah... I installed 2 EG4 18kpv and I wired them like this:

Meter into outside shut offs (200amp x2)...

Shutoffs into each EG4 Grid input

From Inverter load to a 400amp fused disconnected (has two inputs on each side of pull)

From disconnect into electrical panels

This allows both inverters to be in parallel and share the load

1712851431944.png

1712851720702.png

1712851730111.png
 