I just received the following response from Phocos regarding my 'undersized' generator. Based on this response, it looks like the inverter won't be able to pull current from the batteries when the Genset is running. If that's true, when there's no PV current coming from the panels, if I have the Genset running (to charge batteries), my AC loads would be limited to the capacity of the generator. Does that seem odd to anyone else?
My questions are in Blue, Phocos responses are in Red.
- Is my Honda EU2200i compatible as an AC Input source with the PSW-H/5kw/120v inverter/charger?
- In cases where my PV panels are not able to keep up with my energy use, I’d like to be able to use my EU2200i for charging the batteries while maintaining the full capacity of my 5kw inverter. Can you confirm that this is possible?
- Does the PSW-H allow a generator to ‘assist’ the inverter with high loads? That is, will the system’s total AC output capacity be increased by running the generator?
"We don’t recommend such low gensets if your loads are 5KW or more. That’s the reason we specify 7.5KW in the webinar (1.5 times the rating of the inverter). The PSW cannot limit the AC input current delivered to the loads (there’s just a relay in between). A combination of solar and genset to power the loads is possible, but if the panels are not able to keep up with your energy use (cloud, night time) then the genset might be too small for your loads so you will not be getting the full capacity of the inverter 5KW (only the ~2kW of the genset will be used).
The overload bypass of the inverter (when enabled) can switch on the AC input to assist (say 5kW from solar and the excess required from the load can come from the AC input) but we have never tested this for gensets of this size (1.8kW I believe the EU2200i is)."