great to hear, I am about to wire mine up too, your info helps, got to figure out the setup, did you find any youtube on it? like to watch than read a 200 page book
Hooking up one or several Sunny Island is simple enough. Most of those 200 pages cover many parameters. The quick-start menu walks you through basic settings, just need to look up what choices mean (e.g. 2phase4 is 4 Sunny Island, two per phase).
Electrical is fairly basic if you understand what it is supposed to do and know wiring resistance, ampacity, fusing requirements.
I got away with a single 3/4" flexible conduit to each SI for AC. It carries one ground, one neutral, two hots (utility grid and island grid.) Two inverters each had conduit to a "T", then 1 1/4" conduit to another "T" joining two pairs of SI, then 2" conduit to to a "T" connecting breaker panels for utility grid and island. The wires could have all passed through Sunny Island on the way from utility grid to island, with separate ground and neutral each way through separate 3/4" conduit, but I routed the output back parallel to the input through the same conduit. (Neutral will only carry difference in current between grid and island, and difference between SI on two phases.)
The key if you stack two SI on the same phase, and are on-grid not off, is that resistance of parallel wires have to be identical because that's the only thing that causes current to split equally. Each SI can handle 56A, but with two in parallel if total 112A is drawn, it'll never be perfectly matched. Either one SI will have to source some current to stay below 56A or it'll disconnect from the grid (same for feeding PV in to grid, but with battery full all it could do is disconnect.)
I'm sometimes seeing 25% to 33% imbalance when I read the display on Slaves. I suspect a circuit breaker has greater resistance than 60' of 6 ga wire, and imbalance between two breakers causes imbalanced current. I'm investigating "conditioning" the new breakers by cycling them many times, alternate model breakers, fuses instead, and other techniques. My setup can tolerate some imbalance because I programmed 90A maximum due to 100A fused circuit branching to two separately fused 6 ga rather than 4 ga circuits (ampacity derates with several wires in a conduit.) Max imbalance 56A & 34A if resistance ratios 1.65:1 would still deliver 90A.
I did view SMA's video on communication between Sunny Island and Sunny Boy. Oversimplified. I prefer to read manuals, see which jumpers are needed. One document "rs485cabling1-42686.pdf" shows the details needed. It assumes you'll have a monitoring device (e.g. Sunny Boy Control) which will have the needed pull-up & pull-down. If not used, you need to install those jumpers in one of the Sunny Boys. At least with my short wires it's OK to keep the jumpers installed in the Sunny Boy whether or not the monitoring device is connected.
Another issue I had was 10000TLUS-12 was not found by by Sunny Boy Control even though SWR-2500U was found. Maybe would have worked with newer firmware? I installed Web Connect (Ethernet) module, used a router & laptop with Sunny Explorer to see and set parameters (needed Grid Guard code, also PUK to bypass password and change.) The default = UL1741 vs. Island were under Grid Monitor menu. backup = In All Phases was under Device menu. Frequency Start/Stop were under AC menu (just checking, didn't need to change frequency limits.)
So far, frequency shift control of PV inverter output has only worked with "Island" not "Backup" setting. SB does recognize RS-485 commands and switches to off-grid frequency range with "Backup", but doesn't reduce power output. Haven't heard back from SMA if that is a known issue, is limited to 10000TLUS-12, or if other models have the same issue. The new SB7.7-1SP-US-41 are only going to work with "Island" because they don't have RS-485. For European model SI, WebConnect is supported. Maybe that will come to the US, but probably for the 6.0H and 8.0H only, if another poster is correct that SI-6048 is to be replaced with those.