Yes.
12.9V is not very charged.
The battery needs to be FULLY charged before using.
14.4 to 14.6V
Exactly ..... why would we be making recommendations about soft starts and another pack when we already know this pack is at a low SOC and simply may be getting a voltage sag which is kicking out the inverter because of that?
 
I don't see anywhere where we determine how much the fridge is actually drawing on a surge.
We are doing differential analysis between the inverter and the bms with tools that the user probably has on hand.
If the heater starts and runs for more than a few seconds then it points to the bms tripping on over current.
 
We are doing differential analysis between the inverter and the bms with tools that the user probably has on hand.
If the heater starts and runs for more than a few seconds then it points to the bms tripping on over current.
Sorry, but I think we are just shooting blind if we don't know what the fridge is actually pulling.
 
Exactly ..... why would we be making recommendations about soft starts and another pack when we already know this pack is at a low SOC and simply may be getting a voltage sag which is kicking out the inverter because of that?
His inverter has a low voltage shut down at 10 VDC and an alarm at 10.7VDC. An alarm wasn't mentioned so I half suspect the fridge's peak draw pulled the battery down so fast that the battery's BMS shut down before the inverter even sees the drop and has a chance to sound an alarm.

I do agree more testing and facts are needed before spending more money based on assumptions but the consensus does seem to think it is the battery.
 
His inverter has a low voltage shut down at 10 VDC and an alarm at 10.7VDC. An alarm wasn't mentioned so I half suspect the fridge's peak draw pulled the battery down so fast that the batterie's BMS shut down before the inverter even sees the drop and has a chance to sound an alarm.

I do agree more testing and facts are needed before spending more money based on assumptions but the consensus does seem to think it is the battery.
Its might be both.
 
His inverter has a low voltage shut down at 10 VDC and an alarm at 10.7VDC. An alarm wasn't mentioned so I half suspect the fridge's peak draw pulled the battery down so fast that the batterie's BMS shut down before the inverter even sees the drop and has a chance to sound an alarm.

I do agree more testing and facts are needed before spending more money based on assumptions but the consensus does seem to think it is the battery.
He said the voltage is dropping to 12.7 .... but I don't think we really know what the instantaneous drop may be.

When I am troubleshooting .... I always resolve problems as I find them and then retest to see if additional issues exist .... In this case, fully charge the battery and then see what we've got.

There may well still be a problem with surge, but we don't know til we resolve the low charge on the battery.
 
Last edited:
His inverter has a low voltage shut down at 10 VDC and an alarm at 10.7VDC. An alarm wasn't mentioned so I half suspect the fridge's peak draw pulled the battery down so fast that the battery's BMS shut down before the inverter even sees the drop and has a chance to sound an alarm.

I do agree more testing and facts are needed before spending more money based on assumptions but the consensus does seem to think it is the batt
 
my lead-acid batteries were doing the same thing but the inverter would go down to 11.5 then the alarm would go off and it would restart.
 
Sounds like your old batteries were weak also.
 