OK, not sure I understand what the standby mode is or how it is triggered. We don't use the Solis app, so don;t have those coloured icons to look at, sorry.
probably!I see 3 options:
1. Nothing will happen and DoD will be ignored.
At 15% that happens, but only 1% per 5 hours is used by the inverter, so will have PV input before then2. Battery will stop feeding the house at 16% but will start feeding just the inverter at the constant 9W-29W rate all the way down to your forte charge of 10%.
Don't think that is technically possible. AFAIAA the inverter can only be powered by DC input.3. Battery will go to standby directly, with 0W consumed from battery, inverter will convert from AC to DC for its own needs.
Don't think that is technically possible. AFAIAA the inverter can only be powered by DC input.
It discharges to 30% after Backup Mode is activated. After that
the battery is discharged with about 30W (measured). At 27% it recharges from the
Grid and switches off the battery completely at 31% (0A). The Solis is
now supplied with approx. 25W from the Grid. (measured with extra Eastron
counter between Solis and Grid) As far as completely satisfied with the
behavior. Unfortunately, it no longer charges the battery at all. Backup mode off and on fixes the problem until the next night...
No!If I physically unplug my battery to the inverter , it does stay up even if is overnight without PV.
No!
It will act as a Solis Gridtie inverter and powers down when the array voltage falls below 75V
One thing I did note is a change in the commissioning procedure between version 1.1 of the manual (the version on the supplier website) and version 1.5 of the manual (latest from Solis).
v1.1 says turn on the AC first and do all the settings, then close the DC battery isolator.
v1.5 says turn on the DC first, sort out the grid settings (e.g G98/G99 etc) then enable the AC.
I originally though this was just a change of procedure to ensure the grid settings were set correctly before making the grid connection, but I decided to follow the v1.1 manual route because that felt safer re getting battery settings sorted out before connecting a battery. However I couldn't get any life out of the inverter screen at all with AC only. I had to close the DC battery breakers before I could get the inverter kicked into life.
I think this inverter prefers DC but it can still manage with AC only by converting to DC. Defo the documentation doesn’t say anything about it but this is what I can assume as it stays on as you can see on the pics.Then, if your inverter will power up with AC only (i.e. without PV or battery connected), I guess the S5-EH1P is a newer version of the RHI inverters we have and it can be powered via AC. If that's the case then Solis haven't kept their support site up-to-date.
Having re-read this thread, after our discussions on 'your' thread, @finalbillybong, I see that @shavermcspud on page 2 above only had this issue with the 6kW version of the Solis and not his 3kW one. Mine, as you know, is the 3.6kW version and doesn't exhibit this behaviour.Count me as another that is having this problem.
Oh good spot. I will add this information to my ticket with Solis....Having re-read this thread, after our discussions on 'your' thread, @finalbillybong, I see that @shavermcspud on page 2 above only had this issue with the 6kW version of the Solis and not his 3kW one. Mine, as you know, is the 3.6kW version and doesn't exhibit this behaviour.
So the question I'd be asking is... is it a firmware issue and has anyone on this thread or other similar threads got it resolved with a firmware update (or downgrade!) ?
What settings do you have exactly? Self use, Backup..Hello pm2000,
Unfortunately, I have not followed the thread, since I was apparently the only one with the problem occurred. No charge of the battery in deep sleep mode....
Now I read that you have the same errors and a solution to it.
We have researched in parallel and have found different solutions. My solution is to allow 100W feed in the export Power Manager. I have a RHI 4.6kw with the FW 3A0032. Your work around to disable the backup output does not work for me unfortunately.
Maybe it helps one...
??...The 100w Change also put my Battery in today.
100w Export Change from 0 Watts let the Battery wake up. Strange behavior.