Thanks! Now that I've thought about this I've realized I can just put all my 16 cells in series forming a 48v system. Even better since I can then use cheaper hardware and and charger.No... the BMS will expect all the cells in series.
Thanks! Now that I've thought about this I've realized I can just put all my 16 cells in series forming a 48v system. Even better since I can then use cheaper hardware and and charger.No... the BMS will expect all the cells in series.
What the benefit of the second updated photo from the first? Is there more ah's?With 16 LiFePO4 cells, you can get 24 volts a couple ways:
View attachment 7074
Edit: Updated 2P8S image
View attachment 7076
This gets into the old debate of Serial-First (The first photo) vs parallel-first (The 2nd photo) At the top level there is no difference. However, there are pros and cons to both layouts. I prefer the second because of the simplicity (Only one BMS). Others prefer the first because of the redundancy (2 BMSs) and the ability to watch individual cells. You may want to look at this resource. I try to lay out some of the pros and cons.What the benefit of the second updated photo from the first? Is there more ah's?
Another downside of the 2p8s configuration is that the BMS will have to balance cells that are effectively twice the capacity.What the benefit of the second updated photo from the first? Is there more ah's?
With 16 LiFePO4 cells, you can get 24 volts a couple ways:
View attachment 7074
Edit: Updated 2P8S image
View attachment 7076
Two things caught my eye.So. How does this look and am I matching up equipment properly?
View attachment 131463
Two things caught my eye.
1) Check the voltage limits on the charge controller input and make sure it can handle the voltage from 10 panels in series. Note: Be sure to adjust for cold temp when calculating the array voltage.
2) Make sure the breaker on the output side of the charge controller is bidirectional.
Two things caught my eye.
1) Check the voltage limits on the charge controller input and make sure it can handle the voltage from 10 panels in series. Note: Be sure to adjust for cold temp when calculating the array voltage.
2) Make sure the breaker on the output side of the charge controller is bidirectional.
You misunderstood. You need to check your SCCs "max solar input voltage". 10 panels in series is quite high (sum of all Voc for panels in series).1) Per the manufacturer of the charge controller, at 24v, it can handle up to 1040 watts. So I think I'm good there.
Also I was curious if you had any thoughts on what size circuit breaker I should use between the 3000w inverter, and the battery bank? Currently I have a 40amp. In reading online (https://www.renewablewise.com/how-many-amps-does-a-3000-watt-inverter-draw/) it would seem I need a 175amp, which seems excessive to me.
You misunderstood. You need to check your SCCs "max solar input voltage". 10 panels in series is quite high (sum of all Voc for panels in series).
The Voc is what you need to look at. As you put the panels in series, the voltage adds.I'm assuming you mean "max VDC", on the SCC it is 100VDC
I've attached the spec sheet on the solar panel, as I'm not sure what number to look at.
The Voc is what you need to look at. As you put the panels in series, the voltage adds.
View attachment 131468
So 10 panels in series will have a voltage of 243V at 25deg C. As it gets colder, the voltage will go up.
Adjusting Solar Panel Voc for temperature
When designing you solar panel system, it is important to adjust you solar panel Voc for temperature in order to ensure you do not over-voltage the PV inputs of your solar charge controller. This paper shows how to calculate the Temperature...diysolarforum.com
Your SCC can charge at 40A max.So the SCC is too small for this size array at 100vdc,
Max input voltage is one of the more important numbers to consider when buying an SCC and matching panels.since the panels need 243voc,
The controller has a specification for the max voltage it can handle.I find it weird they use two different figures to match systems...
Your SCC can charge at 40A max.
40A x 28V charging = 1120W
Max input voltage is one of the more important numbers to consider when buying an SCC and matching panels.
Since you've already purchased your equipment, you need to look at it the other way around. You need to arrange your panels in a combination of series and parallel to stay below your SCCs max input voltage.
With a Voc of 24.3V you can only get 3 in series to stay below 100V.
A good choice would be to put 3 panels in series, 3 times to make 3 strings. Put these strings in parallel. You can use standard MC4 3:1 Y connectors for the parallel connections.
There is not much you can do with the 10th panel other than get a second (redundancy is good) SCC.
With 4 in series, if the temperature drops very much below 25degC (77F), the voltage will get too high. Please review the resource I linked to in my previous post.I should have thought this through. I think what I will do is use 8 panels, run them in two sets of 4 in series, then run those two sets in parallel. That will keep me under then 100vdc mac and 40amp max for the SCC. THANK YOU!
With 4 in series, if the temperature drops very much below 25degC (77F), the voltage will get too high. Please review the resource I linked to in my previous post.
Short Answer: NOYou're right, 3 in series makes more sense for the cold. I'm in a cold climate, southern Colorado, at 7400 feet, however, what about the fact that there is less sun, and it's at a different angle? Wouldn't that mean there would be less voltage as a result? I can live with 9 panels.
If you don't mind my asking, why didn't you?I should have thought this through.