mangler
New Member
I must got my residential solar system commissioned last week (11.6kw roof mount, Growatt MIN 10000TL XH-US grid tie). I have been getting errors logged on the inverter since the install date. The following errors have popped up:
404(00) EEPROM abnormal (4 days in a row, seems to occur around midnight). Says to restart, but inverter was restarted when this occured on the first day
404(02) bus sample fault Happened on 2 different days, again says to restart
Wondering if any Growatt MIN owners have seen these errors, and if so how they resolved them. My inverter temp also seems a bit high (Hit 58degC with 24DegC ambient, with only 65% load), but that could still be normal (looking for owner feedback). Manual says it will derate at 45degC ambient or above, but no mention of the inverter temperature that triggers the derating. There may be a fan in my future plans (inverter is passively cooled).
404(00) EEPROM abnormal (4 days in a row, seems to occur around midnight). Says to restart, but inverter was restarted when this occured on the first day
404(02) bus sample fault Happened on 2 different days, again says to restart
Wondering if any Growatt MIN owners have seen these errors, and if so how they resolved them. My inverter temp also seems a bit high (Hit 58degC with 24DegC ambient, with only 65% load), but that could still be normal (looking for owner feedback). Manual says it will derate at 45degC ambient or above, but no mention of the inverter temperature that triggers the derating. There may be a fan in my future plans (inverter is passively cooled).