A couple of questions/ brainstorm points…
Why do you have battery charge setting of 40A on batt set screen? Don’t you have tons of PV?
Why are you running a 16s battery at such low voltage settings? (Have you tried 54.4 float/55.8charge/equalize off)
Can you/have you tried having BMS not communicating to SolArk? Let BMS on DIY pack be stand alone?
Have you tried having SolArk use batt V instead of %?
Limited discharge to 100Amp? Total of 2 units x 100A = 200Ax53v only 10kW? Why 2 units? Just for extra PV handling capacity?
Maybe a single 15k unit would have handled loads and split PV arrays up with stand alone charge controllers to not max out a single unit. You’ve got a huge battery bank and looking at settings you’re barely touching it.
Just some thoughts