Unfortunately, on a Cerbo system, the only thing VC is likely to talk to is the MPPT and a BMV-712 or smartshunt. I'm 99% sure the Lynx shunt is NOT BT enabled.
If you have a computer on the same network, opening a browser to
http://venus.local should give access to the remote console of the cerbo, but with a touch screen there's no real advantage to it.
Based on what I see:
Dual Quattro 48/5kVA
MPPT 250/85 connected to Cerbo via VE.Can
Lynx shunt on VE.Can
I would presume the Quattro system is between the shore power/generator and the 12V system, i.e., the stock or similar converter w/12V battery is still in place rather than having a 48-12V converter. This is my preferred method.
I have a highly similar setup:
2X exact same inverters setup for 120/240VAC split phase
MPPT 250/100 on ve.direct instead of 250/85 on VE.Can
BMV-702 on ve.direct instead of lynx shun ton VE.Can
@Ariel188
Please take a picture of:
The front of each inverter where I can see the wired connections.
If it has power, your touch screen showing the pictures of the various devices. Will look similar to this:
I charge my system with a cheap crappy $400 Predator generator from Harbor freight. With the appropriate pictures, we can likely identify your system configuration and provide instructions for connecting a generator either on a DIY basis or to provide additional information to a professional electrician.