What measurement device did he use?
I think the proper way is to apply two different impedances, measure change in grid voltage.
SolarAPP+ wanted me to go through additional effort if grid was capable of more than 10kA. My main breakers are 22kA. But I think the neighborhood Pole Pig is only 25kVA or so.
This was around 1981 if I remember. He was a brilliant engineer, very intelligent, but bipolar.
He likely measured (estimated) the resistance of his hammer-induced short-circuit (milliohms), then measured the AC voltage across it with an oscilloscope (at the time of the short). This allows a calculation of the current as a function of the reduced momentary AC waveform. From that, a rough calculation of the source impedance of the power grid at his location can be done. He did the shorting/measurement process several times, he told me - bang!
I had one case where APS was giving us the "run around" because I was told to let the electrician design the interconnect (backfeed) solution, and he came up with something I knew APS would not normally accept. Then, I had to use a special procedure to calculate short-circuit current after APS (additionally) started insisting everything be rated 22 kA, which was not necessary. After my calculations, they dropped that. However, we had to replace the mobile home service with a more-normal 200 A service that would accept a backfeed circuit breaker, which is what APS wanted. Anything esoteric like a line side-tap feed would be impossible with APS. I made four different versions of that drawing. System got installed, finally. Ground mount system, Cave Creek, AZ.
At one point, for some reason, APS would no longer accept a certain model Square D 60 A disconnect switch, even though rated at 10 kA. I understand - none of this stuff can fail or there is disaster.
I had SRP (Salt River Project) come to my TV Transmitter site one night at 4 am (they insisted) to repair some "closers" on our power pole we noticed were sparking - we reported that late at night and were surprised they came in the middle of the night to do the repair (switched to backup generator during repairs). High current and voltage is taken seriously.