Victron charge settings

Haze

New Member
Joined
Mar 6, 2021
Messages
115
I need help confirming these settings for my 48V SOK battery . I’m wondering if there is better settings to run this at for charging. Thanks

1710442773013.jpeg
 
Does SOK not have suggested settings?
I read the manual and asked the vendor , this is all current connected shared with me when I spoke with them .

Absorb 57.6
Float 55.2
Turn on lithium battery charging on your Multi Plus.

The manual says to do other stuff but just wondering if folks running this battery have similar settings.
 
55.2V absorption (3.45V/cell)
1-2 hour fixed; longer if not getting to sufficiently high SoC.
54.0V float

If charge speeds are slow, adjust absorption up and time down. These are my typical limits:

55.2V absorption, 2 hours for slow charging
57.6V absorption, 15 minutes for fast charging.
 
Do you have a temperature sensor on the charger?

If so… enable the low temp cutoff at around 38F - that’s probably well below what the battery will ever see. I always use low temp charging cutoffs above the bms cutoff temp point.

Do you only have one 100ah 48v battery? If you have more than one then raise the current charge - but for one battery 30a is a .3C charge - which is where I would have it.

I use a lower float on my 12v battery 13.5v = 3.375v per cell - = 54v
 
Do you have a temperature sensor on the charger?

If so… enable the low temp cutoff at around 38F - that’s probably well below what the battery will ever see. I always use low temp charging cutoffs above the bms cutoff temp point.

Do you only have one 100ah 48v battery? If you have more than one then raise the current charge - but for one battery 30a is a .3C charge - which is where I would have it.

I use a lower float on my 12v battery 13.5v = 3.375v per cell - = 54v
I have it set lower because I’m charging from a wall outlet in my old house right now and I’m afraid to pull to many amps. Yes I only have one so far, will be getting another next week.
 
I have it set lower because I’m charging from a wall outlet in my old house right now and I’m afraid to pull to many amps. Yes I only have one so far, will be getting another next week.

Definitely use the long slow charge settings. You also need to set the AC input limit according to the house circuit. With this set, it doesn't matter how high your charge current is. It will not pull more charging than can stay within the AC input limit.

General tab:

1710450769863.png

If you're charging on a 15A circuit, set for 13.5A
 
Post up a picture of how you have the MPII mounted with the BT module, people need ideas, hahah.
 
When will you be getting your Cerbo? That's when the real boners hit.
I have the cerbo already hooked up, unfortunately I’m to dumb too understand 90% of what it can do.

I can't get over how neat this solar is…you all are bad influences on me. Now I need more panels…I can see this is going to be an expensive hobbie.
 
Post up a picture of how you have the MPII mounted with the BT module, people need ideas, hahah.
It’s sitting on my wife’s dining room table as we speak. Next week I’m going to load it all up in my snow cat and try to get into our cabin. Might be a few weeks before I get it all mounted but, I will get pics of it as soon as possible.
 
Ok I’m now onto setting up the MPPT side of our system. I have one Victron 450-100 , I’m wondering how many of these panels can I run in series ? Our cabin does see freezing temps since we sit right above Lake Tahoe. I want to play it safe so I was thinking 4 panels in series on each controller . Am I missing something, or does this look ok. Thanks IMG_9784.jpegIMG_9783.jpeg
 
looks good to me. appears to be over the 120vdc start up voltage. How many panels are you installing?
I was going to go with 4 in series on each tracker just to play it safe the first year.
 