I have run almost 1MWh through the 18k+ 2x PowerPro (400A, 20kW peak) Batteries + 18kw panels and it’s been working great (mainly off grid). Now that we are hitting a couple hot days in Texas I have tried to use my 4ton lennox xp21-048-230-04. It will not run while I have the inverter disconnected from the grid. I have purchased a soft start and will go into details.
The units RLA=21A(5kW) and LRA=104A(25kW). After installing the soft start I read ~41A(10kW) peak startup while on grid power (By grid power I mean grid connected through 18k to the load) and everything runs fine. This is within the capability of the inverter so that’s expected.
After this testing I turned off my grid disconnect(running on batteries and solar) and the air conditioning will not startup and run. I thought this was odd so I re-connected the grid and the ac started up fine. I let it run for a few minutes and the data shows that ~5kW is being pulled from the batteries as expected with no grid power being used. Now I turn off my grid disconnect and the air conditioning shuts down. I can’t figure out why the 18k can’t keep the air conditioning running while it is in its 5kw steady state or why it is not capable of starting it with the soft start.
My 2-ton unit runs on the 18k perfectly fine with grid power turned off.
My dad is working through the troubleshooting process with signature solar, but wanted to see if anyone here could help.
Firmware version is fAAB-1717
The units RLA=21A(5kW) and LRA=104A(25kW). After installing the soft start I read ~41A(10kW) peak startup while on grid power (By grid power I mean grid connected through 18k to the load) and everything runs fine. This is within the capability of the inverter so that’s expected.
After this testing I turned off my grid disconnect(running on batteries and solar) and the air conditioning will not startup and run. I thought this was odd so I re-connected the grid and the ac started up fine. I let it run for a few minutes and the data shows that ~5kW is being pulled from the batteries as expected with no grid power being used. Now I turn off my grid disconnect and the air conditioning shuts down. I can’t figure out why the 18k can’t keep the air conditioning running while it is in its 5kw steady state or why it is not capable of starting it with the soft start.
My 2-ton unit runs on the 18k perfectly fine with grid power turned off.
My dad is working through the troubleshooting process with signature solar, but wanted to see if anyone here could help.
Firmware version is fAAB-1717