Live Ground Shocked 5 Year Old

I think we could still use detailed wiring pics. There's all sorts of possibilities and people jump to conclusions especially about grounding and bonding.
 
More info: If your autoformer were to fail or pop it's breaker, you would apply 240v to all your 120v appliances... is it worth it? A wife flipping the wrong breaker for example could cause the microwave and fridge to get fried.... is it worth it?
Auto transformer looks hard wired into 120v loads panel (right panel). Flipping its breaker (left panel) would remove both L1 and L2 so no chance of 120V loads being unbalanced.

Big question for @Joshua787 is the ground rod connected to Growatt's ground and is there a neutral to ground bond at the breaker panel? My guess is the neutral to ground bonding screw is in place inside Growatt and no N-G bond in the panel. This will bias the neutral to 120Vac in relation to earth ground. So L2 is actually at earth potential, N is at 120V and L1 is at 240V. This is probably why you were measuring live voltage in the outlet with breaker turned off. Your neutral to ground had 120V.
 
Last edited:
Thank you for the concern, much appreciated. I disconnected completely the outlet and wire that ran to the metal box screwed to the shipping container to limit the circuit to just the inverters, circuit breaker panels and transformer. This would allow me to trouble shoot within that specific space. Ive been reading up and the issue seems like its a ground/neutral bond from the inverters. Apparently there is a US version and a European version.
Just a quick follow-up to my advice I offered. I fed my family working as an electrician giving me enough knowledge to know I can't walk you through this online and be 100% certain of your family's safety.

To those posting help do you feed your family doing electrical work? or is this a hobby? The OP has a right to know just how much you really know.
 
To those posting help do you feed your family doing electrical work? or is this a hobby? The OP has a right to know just how much you really know.
DIY is the name of the forum. Everyone here is tacitly accepting the risk of their own actions and understanding the nature of the advice received.
 
Last edited:
Nope.

But how many electricians understand inverters? Or the nuances of auto-transformers?
Besides, I'm "experienced".

I agree it is best to have someone who understands these things to check it over and debug in person.
For many of us here, that would be ourselves. Even better to get a second opinion.
 
"grounding" the container will not stop it from being a shock hazard. Bonding and grounding could.

That's why we keep telling people they need a wire that bonds PV panel frames to inverter chassis. Not just a separate ground rod at the frames.

The two most likely issues with OP's system are
1) PV frames have AC capacitively coupled to them because inverter imposes AC on PV+/-
2) Inverter has one of its two 240V legs bonded to chassis, and auto-transformer center tap ("Neutral") has a path to earth (i.e. is "grounded"). As Antron describes.

Adding a separate ground for the container could mean two ~ 25 ohm connections to earth, with current running through them.

Ideally we would get to see a schematic of entire system.
 
Last edited:
Just a quick follow-up to my advice I offered. I fed my family working as an electrician giving me enough knowledge to know I can't walk you through this online and be 100% certain of your family's safety.

To those posting help do you feed your family doing electrical work? or is this a hobby? The OP has a right to know just how much you really know.

First, this is DIY.

Second, it is pretty arrogant of you to assume nobody here knows anything about this sort of problem.

Many here have practical experience and more than enough education to know what they are saying. I know I wouldn't give advice in here until the OP posts back pictures and a wiring diagram so I wouldn't give a wrong answer.

I can see your point that the OP should carefully consider the advice he is given before doing things. And be double careful about testing before letting his famliy near. But it doesn't take a certified master electrician to track down an issue like this.
 
You don't have a N/G bond.
And I'm pretty sure he's got no NG bond at the breaker panel. Having NG bonding screw in Growatt and NG bond at the panel would cause a short circuit through the autotransformer and trip the inverter.
 
Last edited:
This is a very specific niche in the electrical industry, I attended a trade highschool in CT so ive been electrical work since i was a teenager, i am now 40 yrs old, lost a year here and there in 2008 and a year in the .MiL, but the rest is all high end homes, lighting control, generators, landscape lighting, service changes...lots and lots of service changes. But my solar knowledge pertaining to the inner workings and nuiances of each manufacturer make me low on this totem pole. General electrical practices will still spill over..
the side job electrician hed prolly find Wouldnt know what to do, and if he's the fake it till you make type would prolly smoke something in the process of poking around.
 
And I'm pretty sure he's got no NG bond at the breaker panel. Having NG bonding screw in Growatt and NG bond at the panel would case a short circuit through the autotransformer and trip the inverter.

Only if chassis of Growatt does connect to chassis of auto-transformer.
I can't make out color of wires and connections well enough in photo with breaker panel.

Unfortunately, I'm experienced at mis-connecting chassis. Good to check between all boxes for volts, and for ohms.
 
First, this is DIY.

Second, it is pretty arrogant of you to assume nobody here knows anything about this sort of problem.

Many here have practical experience and more than enough education to know what they are saying. I know I wouldn't give advice in here until the OP posts back pictures and a wiring diagram so I wouldn't give a wrong answer.

I can see your point that the OP should carefully consider the advice he is given before doing things. And be double careful about testing before letting his famliy near. But it doesn't take a certified master electrician to track down an issue like this.
Not in the least just look at the wide variety of answers thrown out there from the armchair DIYers. Every response should have first asked and received more information before making their wild a** guess based on what they think they know. It's called the Dunning-Kruger Effect.

End of rant
 
And I'm pretty sure he's got no NG bond at the breaker panel. Having NG bonding screw in Growatt and NG bond at the panel would case a short circuit through the autotransformer and trip the inverter.
Exactly
And instead of the breaker or inverter protection doing what it's supposed to.
Everything that should be grounded is live.
 
Not in the least just look at the wide variety of answers thrown out there from the armchair DIYers. Every response should have first asked and received more information before making their wild a** guess based on what they think they know. It's called the Dunning-Kruger Effect.

End of rant
I don't need any pictures to know what the problem is.
But that's because I am familiar with their equipment.
And 40 years in the trade , doesn't hurt.
 
Detailed pictures of each panel and device wiring would help.

Please…

Before you attempt ANY troubleshooting, get good lighting, and take detailed pictures of everything connected to the container, let us see the boxes, wires junctions everything.

We may see the issue right away, and save you a lot of headache.
 