Live Ground Shocked 5 Year Old
If everyone reads the first post.
OP states he is reading 120V between hot and ground.
This is correct.
He says that the breaker feeding the hot was off, and he STILL reads 120V
This is wrong, and dangerous.
What OP does NOT ever state is what the child was shocked by touching.
Nor does OP say much other than with the box disconnected from the container, there is no more shock.
I would like a post stating measurement facts.
1. What meter reading is reached between Neutral, and the container wall.
2. What meter reading is read between container wall and the ground connection.
Both Volt reading, ac AND dc, and an ohm reading IF and ONLY IF the volt readings are zero.
Grounding conductor should never pass through any metal enclosure. (Inverter, service panel, junction box, wireway)
It should be connected to all conductive parts. This makes these parts safe to touch.
But, that's only true if the grounding system is actually bonded to the electrical system. (N/G bond)
The grounding system is created by and begins at the N/G bond.
Which takes us back to my first post in this thread.
"Short answer.
Your system is not properly grounded.
You don't have a N/G bond."
The fact that the wrong (European) version of Growatt was used, would not have caused the shock. (If the system was properly grounded)
Because it would have never powered up, in the first place.
@Joshua787 OK, thanks. Could you use a multimeter to verify which pin on the jumper power cord actually connects to shipping container? Also check if plug pins are correctly wired to 2nd outlet.
Correct
Not the same conductor.
The European neutral is your L2 hot. This needs to be unbonded.
Your split-phase neutral from the transformer needs to be bonded.
THANK YOU SO MUCH!!!! I removed the bolt and it worked!
You said "Your split-phase neutral from the transformer needs to be bonded." How do I do that? do you think this would solve the problem below?
NEW PROBLEM:
Im experiencing Voltage Leakage. When the 20A breaker is ON it reads 81V instead of 120V when I measure from Ground to Hot (See pics)
When the 20A breaker is OFF - i measure 33V from Neutral to Ground and 18V from Hot to Ground.
View attachment 207065View attachment 207068
The green wire was grounding the box to the second outlet. this was done by striping the wire and wrapping it around the self tapping screw that attaches the box to the shipping container. i left a tail on the ground wrapped around the screw that is wrapped around the ground screw on the outlet.
Great! Now with inverter NG bond screws removed you need to create neutral to ground bond in your right panel. Connect with a piece of wire as shown in blue. Connect ground wire to your container to make sure it never goes hot again. Connect ground wire to ground terminals of both inverters.
NEW PROBLEM:
Probably no neutral-ground bond. There is capacitance, and DMM measures voltage divided by capacitors in series.
It sounds like you isolated inverter "N" (one of your "L") from ground. You said "bolt", but I suppose you mean a screw through inverter PCB into chassis; that was all the rage a few months back.
You would ideally have a detailed schematic, maybe made with photos of equipment taken from websites, showing all wires L1, L2, N, G connecting everything. Also showing any (typically green) bonding screws which are used in breaker panels to connect Neutral bar to box for use as combined neutral and ground.
So far your photos have shown wires passing through some boxes. All need chassis ground.
You may get it apparently working but still have latent safety issues. Ungrounded boxes could become shock hazards in the future, if not grounded so a fault causes inverter to shut down.
I would also bond solar panel frames together and connect them directly to ground rod via dedicated #6 solid copper direct ground wire. Also connect shipping container to same ground rod via it's own wire for redundancy. This way if your solar panel frame gets struck by lightning it will route strike current direct to ground rod instead of traveling through that original ground wire in your conduits.
NEW PROBLEM:
Did you consider reading the replies with a focus on comprehension and MOVING the ground-neutral bond from the wrong place to the right place?
I take that to mean she was standing on the ground and touched outside of container.
Yea I think the shock was superficial due to capacitive coupling between components. Inverters were ungrounded and floating.
There are a few ways to accomplish this.
But basically the neutral and ground need to be connected together.
A piece of green wire will between the two bars is a simple way.
So inverter output tied to chassis.
But there was a ground rod, I think. Not sure what connected to.
I'm not confident that shock current was limited by capacitance. With all the wires and connections or lack of them, a source of hazardous current may be present. Or not. Current could have been limited by rubber shoes (what I usually, but not always, have "experienced".)
Your suggestion of a light bulb (did you plagiarize that from me?) shows if there is a hard path, but of course isn't sufficient to distinguish safe current from hazardous.
I've suggested light bulb to see if a cheap inverter could have neutral bonded, or was 60/120V split-phase.
These days I have to clarify "incandescent", since without understanding they're likely to grab a "light bulb" which doesn't accomplish our measurement objective.
Now that the L2 bonding is removed, and you are still getting odd readings with a meter, the next step is to create a proper grounding system.
All ground rods need to be connected to the EGC conductor, and it needs to be correctly fed to the main panel, and bonding conductors need to go from the main Ground terminals to EVERY METALLIC COMPONENT IN THE SYSTEM.
BE SURE BOTH INVERTERS ARE OFF FIRST.
Run full size grounding conductors to each panel or equipment cabinet and to the container. Not with a tapping screw, with a hole drilled in the container, a bolt run through the container, with any paint removed around the bolt, and a proper lug attached to the bolt, and the grounding conductor fed to the lug.
In the panels, use the grounding terminals, not a screw through the cabinet.
AFTER the grounding system is bulletproof, and all equipment and metal components are bonded to the grounding system, go to the FIRST disconnecting means with a true Neutral in it, and connect to the grounding system here.
ALL neutrals outside this box must be isolated from ground.
Just a quick follow-up to my advice I offered. I fed my family working as an electrician giving me enough knowledge to know I can't walk you through this online and be 100% certain of your family's safety.
To those posting help do you feed your family doing electrical work? or is this a hobby? The OP has a right to know just how much you really know.
This actually kind of ticks me off. I had just commented a few weeks ago that what is so amazing about this forum is that we DO have many qualified people on here who DO go out of their way to offer help. I can go to any electrical forum and get the standard "hire an electrician, you aren't qualified."
Not only do we have many qualified people on here, we have qualified people with real life experience. Something you won't necessarily find going to your local electrician. And, beyond that, even people who aren't electricians sometimes contribute because they've dealt with identical situations.
So, the OP could have left this sit until his local guy could take a look and hopefully understand the situation, (likely not, as it was partially an inverter situation), and risk possibly worse injury, or hop on here and get instant help that may have prevented that.
Spend some time reading what these guys post. You'll see that this forum doesn't need electrician police.
This actually kind of ticks me off. I had just commented a few weeks ago that what is so amazing about this forum is that we DO have many qualified people on here that DO go out of there way to offer help. I can go to any electrical forum and get the standard "hire an electrician, you aren't qualified."
Not only do we have many qualified people on here, we have qualified people with real life experience. Something you won't necessarily find going to your local electrician. And, beyond that, even people who aren't electricians sometimes contribute because they've dealt with an identical situations.
Id be curious to know how many electricians or companies would even take the call. Off grid solar, diy installed, shipping container - likely result in several "sorry, too busy" responses or just the phone hung up. This is still a nich market that doesn't have full support everywhere.