I’ve got my entire system set up in a conex box. I set up a uni-strut cage so that I could mount various pieces of electrical equipment. [edited for spelling] Quattro, main panel, cerbo , MPPT, etc. And a large metal shelving unit for the batteries.
All this stuff is bolted together. That is, the Quattro, main panel, etc are attached with nuts and bolts. And the metal bookshelf it similarly attached to the strut.
My earth ground conductor runs to the Quattro.
Everything I’ve mentioned above shows basic continuity on the multimeter. And I plan to run a jumper wire from the ground wire to the conex box itself.
My first question is whether I need to run jumper wires to and from each piece of equipment? Some have grounding attachment points, some don’t.
I’m thinking yes, I do need to. The NEC just says “connected together.” They are definitely connected. But I’m not sure whether my incidental connections establish an effective ground-fault current path.
My second question is what is the maximum fault current? 5000/120 for the inverter is 41 amps. The batteries are 48 volt and 100 amps each. How would calculate that? Maybe limited by the 225 amp class T fuse?
Thanks
All this stuff is bolted together. That is, the Quattro, main panel, etc are attached with nuts and bolts. And the metal bookshelf it similarly attached to the strut.
My earth ground conductor runs to the Quattro.
Everything I’ve mentioned above shows basic continuity on the multimeter. And I plan to run a jumper wire from the ground wire to the conex box itself.
My first question is whether I need to run jumper wires to and from each piece of equipment? Some have grounding attachment points, some don’t.
I’m thinking yes, I do need to. The NEC just says “connected together.” They are definitely connected. But I’m not sure whether my incidental connections establish an effective ground-fault current path.
My second question is what is the maximum fault current? 5000/120 for the inverter is 41 amps. The batteries are 48 volt and 100 amps each. How would calculate that? Maybe limited by the 225 amp class T fuse?
Thanks