I don't see that this inverter is UL9540 compliant.This is standard requirement for UL9540 compliant inverters.
My impression is that the battery comm failure happened much faster than those timeouts. I now suspect it is a monetary issue AFTER the inverter rebooted from the power failure. It tends to display battery com failure on first power up and then it goes away.The inverter <--> battery communications must always respond to requests, retries are allowed, but there are timeouts in the 1 to 5 minute range that will trigger the shutdown.
I expect this is not the case. The battery comm failure is a symptom, not the cause.I suspect with painful data logging of the canbus coms you will find there is a request that isn't being responded too and the inverter considers the correctly it is a fault.
The inverter only supports Megarevo protocol (no means of selecting something else). The battery has a compatible protocol selection. It worked fine for 48 hours and is only not working now because I switched to voltage (lead acid) mode to avoid battery comms as a test. I feel confident if I put it back to lihtium mode with comms, it will work fine for battery comms. The underlying bug, the power failure, will remain, however.One would need the actual document for the protocol you are using and log the communications 24/7 to track down what actual address is the problem and then be able to inform the manufacture what they missed. If you can, you should try and use a more common protocol like the Pylontech High Voltage if possible with your inverter and bms if the support this.
I believe the inverter has a built in list of protocols that it scans to see which is compatible. The only reason I think that is because I'm using the pylontech protocol on my server rack battery and it connected right away. You mentioned using the megarevo protocol.The inverter only supports Megarevo protocol (no means of selecting something else). The battery has a compatible protocol selection. It worked fine for 48 hours and is only not working now because I switched to voltage (lead acid) mode to avoid battery comms as a test. I feel confident if I put it back to lihtium mode with comms, it will work fine for battery comms. The underlying bug, the power failure, will remain, however.
That is very interesting.I believe the inverter has a built in list of protocols that it scans to see which is compatible. The only reason I think that is because I'm using the pylontech protocol on my server rack battery and it connected right away.
The Amensolar inverter clearly has Megarevo design heritage, so that is the one I chose.You mentioned using the megarevo protocol.
That would be useful.I'm gonna try and see if I can get a list of compatible protocols.
Here's the list of battery protocols I got from Ian. I know Megarevo isn't on that list and I'm not familiar with most of them.I believe the inverter has a built in list of protocols that it scans to see which is compatible. The only reason I think that is because I'm using the pylontech protocol on my server rack battery and it connected right away. You mentioned using the megarevo protocol.
I'm gonna try and see if I can get a list of compatible protocols.
Got around to taking some measurements on Inv2 today. The second inverter does not show the large error in reporting loads in either the loads or inverter page. It also appears to report the loads correctly to SolarAssistant. Something is up with Inv1.SolarAssistant calculates charge/discharge from the aio? I was under the impression, that everything under the battery tab and the battery gas gauge was whatever the jk bms's send SA.
Remeasured today and found two mistakes, 1) measured one ac line and the neutral, 2) didn't zero the meter. Rerunning the second set of numbers in post#470 knowing about the neutral brings the measured watts at the load1 panel and the measured dc battery draw within a 100w difference. Still way off from what the nhx reports.
From today measured at the load1 panel:
2.36amps@120vac=~283w
13amps@120vac=~1560w
measured battery draw was 34.8amps@53.2vdc =~1851w
concurrently, the nhx display shows:
1.2amps@120vac@126w
6.3amps@120vac@731w
reported battery draw of 34.6amps@53.0vdc=~1834w
No matter how you look at it, the numbers the nhx report are way off.
`
What are the negative consequences of disabling this?So all that to say is if you're experiencing long PV startup times or a random loss of PV in the middle of the day, take a look and see if you have Insulation Detection enabled.
If you are not hooked to grid, which IIRC, your parents are not, then nothing.What are the negative consequences of disabling this?
Why did it not generate an alert/alarm message about this?
My inverter seems not to generate any alert/alarm messages when the grid goes away which I find odd. Is that true for anybody else?
Mike C.
Don't think so. We've had 3 inverter caused LOAD1 drop outs in 3 weeks, at random times, lasting each about 30 seconds, without any obvious external stimulus, and also without any alert or alarms. The very first drop out had a battery comm alert, but I now think that was just a side effect of the drop out, not the cause since we switched to no comms and had two drop outs since.@mciholas could this have been your issue?
Maybe the CTs are the wrong ratio, 2000 to 1 instead of 1000 to 1? That would only affect grid measurements, though.Now I just have to figure out why one inverter is under-reporting Vac loads by ~1/2. Anyone have some ideas?
My parents inverter is grid and battery only for now, no PV yet. Just trying to use it as a backup panel UPS for now.If you are not hooked to grid, which IIRC, your parents are not, then nothing.
Unfortunately the manual doesn't actually explain what the function does, only how it reacts.What are the negative consequences of disabling this?
Before I saw that it was a "feature, I was thinking the same thing. It didn't generate any alarm or warning because its working as it was designed to. The manual tells you that if your off grid you will lose power and if you're on grid it will shift loads to grid.Why did it not generate an alert/alarm message about this?
I don't recall seeing anything for losing a grid connection either. I see a warning when my inverter switches over to grid due to the TOU settings. There might be a "low grid voltage" when I first introduce grid power.My inverter seems not to generate any alert/alarm messages when the grid goes away which I find odd. Is that true for anybody else?
If it randomly drops AC Output during the middle of the day, it could be this "insulation detection" scan running. The manual says it'll run once a day and you'll lose output power if no grid is connected.Don't think so. We've had 3 inverter caused LOAD1 drop outs in 3 weeks, at random times, lasting each about 30 seconds, without any obvious external stimulus, and also without any alert or alarms. The very first drop out had a battery comm alert, but I now think that was just a side effect of the drop out, not the cause since we switched to no comms and had two drop outs since.
I have grid so the power drops don't fit this profile.If it randomly drops AC Output during the middle of the day, it could be this "insulation detection" scan running. The manual says it'll run once a day and you'll lose output power if no grid is connected.
Gotcha. Couldn't remember exactly what the setup was at your folks house (pretty sure that's where you said it was).I have grid so the power drops don't fit this profile.
The time of the drops have been about 6:20 pm for the first two 8 days apart, then one in the early AM about 5 days later (no exact time since no alert is posted). If it was once per day, you'd think it would happen at the same time per day.
The PV wires are run to a junction box and capped, attached to nothing. Hard to imagine that would fail any sort of test by the inverter. The inverter reports their voltage is about 30 volts, which I think is just leakage through the electronics. Maybe I should have shorted PV- to PV+? But lots of folks won't use all MPPT inputs, and leave some floating, so that must work, right?
Mike C.
Curious, turn off insulation detection and see if anything changes. Yeah, it shouldn't do anything but maybe some kind of bug or ...?I have grid so the power drops don't fit this profile.
The time of the drops have been about 6:20 pm for the first two 8 days apart, then one in the early AM about 5 days later (no exact time since no alert is posted). If it was once per day, you'd think it would happen at the same time per day.
The PV wires are run to a junction box and capped, attached to nothing. Hard to imagine that would fail any sort of test by the inverter. The inverter reports their voltage is about 30 volts, which I think is just leakage through the electronics. Maybe I should have shorted PV- to PV+? But lots of folks won't use all MPPT inputs, and leave some floating, so that must work, right?
Mike C.
Could do that. My settings right now:Curious, turn off insulation detection and see if anything changes. Yeah, it shouldn't do anything but maybe some kind of bug or ...?
The only difference on my page is that I turned off Insulation Detection. I'm not sure what the homeload option does either.Could do that. My settings right now:
View attachment 221569
I understand anti island (must be on!), leak current, and insulation detect. I can try turning them off and see what happens.
The manual is useless to understand all the left hand side, though, what do they do? I don't have sell enable checked, so I am thinking all of it has to do with when the inverter can sell back to the grid, so they shouldn't apply to my situation right now.
The manual doesn't even mention Homeload EN. Any idea what this is?
There is a huge gap between what the manual and UI say and a customer's understanding of the exact behavior of the inverter. It would sure help a lot if the manual got rewritten to be VERY precise about what each selection does and how that affects the inverter behavior.
Mike C.
Depending on who they had translate it from Chinese, that could be a better manual.A Dutch South African manual is coming soon![]()
So I ran some tests this morning after talking to @Kornbread and it seems that the "HomeLoad EN" takes any loads you might have from your grid side and adds them to the "Home Consumption" icon at the bottom of the screen. So I'm guessing it actually reads the power flowing through the AC In and then adds it to the Home Consumption.The manual doesn't even mention Homeload EN. Any idea what this is?