Hi folks. I’m dealing with a strange problem and was hoping to get some feedback from more experienced solar system owners, especially those who use buried cable runs from their solar panels to their charge controllers/batteries. Keep in mind as you read this that this setup has worked fine for 2 years.

The setup:
Offgrid cabin location.
Qty 4 12v panels (420w total) arranged in series for 48v. Tested open line voltage at the panels is ~80v in full sun.
~60 foot buried run of USE-2 12awg pv cable. The wire states direct burial, so no conduit was used.
Renogy Rover 60a Charge Controller
Renogy 12v 100ah LiFePO4 battery

The problem:
When we opened the cabin this spring, I noticed the battery wasn’t charging when the sun was out. Voltage coming from the panels measured both by a multimeter on the PV terminals and the charge controller readout was 12.7v. When I disconnected the panel wires from the charge controller to measure open voltage, it measured 80v.

The troubleshooting:
- I first rigged up a ~50 foot length of 12awg wire with MC4 connectors and plugged one end into the solar panels directly and the other into the charge controller+battery combo. The charge controller registered ~80v and the battery started charging. So I know the panel MC4 connectors are OK.

- I replaced the MC4 connectors on the panel side of the buried wire and re-tested. The charge controller showed 12.7v.
- I snipped the MC4 connectors off the controller side of the buried wire and connected them to the charge controller with wire nuts. Controlled showed 12.7v.
- Finally, I snipped the buried wire side 2ft below the newly-replaced MC4 connectors that connect to the panels and wire-nutted them to the charge controller. That showed 80v.

What this seems to tell me is that I have some sort of fault in my buried wire. There are no splices or connections in the buried wire - it’s contiguous.

Has anyone else had a USE-2 style direct burial cable fail? And what might be the symptom here that would show 80v open line voltage but then drop the voltage to a much lower value? Wondering if an animal might have eaten through the cable and it’s now somehow shorting into the ground?

Any ideas from the more experienced crew is greatly appreciated. I’m guessing I’ll have to make a new wire run, but want to know the “why” if possible.

Thanks!
 
I'm thinking a high resistance section would cause the regular open circuit and drop under load, like a partially but not totally severed cut in the wire.
 
Hi folks. I’m dealing with a strange problem and was hoping to get some feedback from more experienced solar system owners, especially those who use buried cable runs from their solar panels to their charge controllers/batteries. Keep in mind as you read this that this setup has worked fine for 2 years.

The setup:
Offgrid cabin location.
Qty 4 12v panels (420w total) arranged in series for 48v. Tested open line voltage at the panels is ~80v in full sun.
~60 foot buried run of USE-2 12awg pv cable. The wire states direct burial, so no conduit was used.
Renogy Rover 60a Charge Controller
Renogy 12v 100ah LiFePO4 battery

The problem:
When we opened the cabin this spring, I noticed the battery wasn’t charging when the sun was out. Voltage coming from the panels measured both by a multimeter on the PV terminals and the charge controller readout was 12.7v. When I disconnected the panel wires from the charge controller to measure open voltage, it measured 80v.

The troubleshooting:
- I first rigged up a ~50 foot length of 12awg wire with MC4 connectors and plugged one end into the solar panels directly and the other into the charge controller+battery combo. The charge controller registered ~80v and the battery started charging. So I know the panel MC4 connectors are OK.

- I replaced the MC4 connectors on the panel side of the buried wire and re-tested. The charge controller showed 12.7v.
- I snipped the MC4 connectors off the controller side of the buried wire and connected them to the charge controller with wire nuts. Controlled showed 12.7v.
- Finally, I snipped the buried wire side 2ft below the newly-replaced MC4 connectors that connect to the panels and wire-nutted them to the charge controller. That showed 80v.

What this seems to tell me is that I have some sort of fault in my buried wire. There are no splices or connections in the buried wire - it’s contiguous.

Has anyone else had a USE-2 style direct burial cable fail? And what might be the symptom here that would show 80v open line voltage but then drop the voltage to a much lower value? Wondering if an animal might have eaten through the cable and it’s now somehow shorting into the ground?

Any ideas from the more experienced crew is greatly appreciated. I’m guessing I’ll have to make a new wire run, but want to know the “why” if possible.

Thanks!
Do you have moles …? Ground hogs…? Rats..? Ground squirrels ..? All of them love a nice salty tasting piece of insulation now and then…
 
I'm starting to think any type of "direct burial" wire is a scam unless it is somehow heavily armored against critters. Put buried wire in conduit or consider it temporary at best.
 
I'm thinking a high resistance section would cause the regular open circuit and drop under load, like a partially but not totally severed cut in the wire.

Yep. Locating direct bury wire faults are one of my many underground utility chores...

Get an extension cord long enough to reach from one end of the 60' to the other. Connect one or more of the cord conductors to one of the PV wires, creating a loop back. At the other end, check with an ohmmeter btwn the PV wires and the cord conductors. One should have low loop resistance. If not, switch to the other PV wire and check that. If they both have low resistance, figure out how to get a load on things and test each wire again. Sometimes direct bury faults don't reveal themselves until you draw current. If only one of the PV wires reads low, and the other much higher, you've found the problem.

Let us know how it goes.
 
If you just wanna do a quick 'n dirty, just short one end of the PV wires together and check the other with an ohmmeter. The above procedure is for isolating the particular wire, which is what I need to do before connecting the fault locator transmitter.
 
I'm starting to think any type of "direct burial" wire is a scam unless it is somehow heavily armored against critters. Put buried wire in conduit or consider it temporary at best.
How deep did you bury it? Should be 24 inches, and covered with sand. That cuts down on critters. I buried mine 6 inches in RMC to eliminate critter risk, and so I didn't have to dig so deep.
 
2jvoly.jpg
We have replaced our ftth cable more times than I can count due to squirrels I feel for you op.
But for future reference even if the cable is direct burial, conduit is always best as you only need to dig once and then if any issues appear you can replace cable as needed without having to dig again.
 
Do you have moles …? Ground hogs…? Rats..? Ground squirrels ..? All of them love a nice salty tasting piece of insulation now and then…
We have muskrats and minks along with turtles and all manner of lake birds.
 
How deep did you bury it? Should be 24 inches, and covered with sand. That cuts down on critters. I buried mine 6 inches in RMC to eliminate critter risk, and so I didn't have to dig so deep.
I buried the wire 12 inches deep. I figured that there wouldn't be any critters down a foot in the dirt and there's no evidence of chewing on the wires that are exposed.

I'm feeling from this thread that I'm greatly underestimating the chew habit of critters!
 
If you just wanna do a quick 'n dirty, just short one end of the PV wires together and check the other with an ohmmeter. The above procedure is for isolating the particular wire, which is what I need to do before connecting the fault locator transmitter.
Great idea. I'm reasonable with electrical setup, but still learning quite a bit at electrical troubleshooting. I will try this, thank you!
 
Yep. Locating direct bury wire faults are one of my many underground utility chores...

Get an extension cord long enough to reach from one end of the 60' to the other. Connect one or more of the cord conductors to one of the PV wires, creating a loop back. At the other end, check with an ohmmeter btwn the PV wires and the cord conductors. One should have low loop resistance. If not, switch to the other PV wire and check that. If they both have low resistance, figure out how to get a load on things and test each wire again. Sometimes direct bury faults don't reveal themselves until you draw current. If only one of the PV wires reads low, and the other much higher, you've found the problem.

Let us know how it goes.
Thank you! Appreciate the guidance. As I noted in another reply, troubleshooting is still something I'm learning.
 
Next time just use somting to save the cable like a brick with holes .
Stick it in the ground.
Save the cable .
Well you can diy project with a drill and make a hole.
 