With the generator you have, inverter and batteries are essential, and a good inverter will let you run your generator at peak efficiency when it runs. Then expand panels as you can. That will be your long-term outage power supply, and you can try to minimize generator use to stretch your propane supply.

Figure cloudy day with MPPT is still going to be 1/3 of your sunny day output - and for off-grid that's the number that matters more. If you've got AC, you probably care less about it on a cloudy day, which is a good thing.
Yes, minimize the generator usage. Instead of running to power the home just run it to help charge the batteries. Open to more choices on inverters, what do you own?.
 
Bones1 said:
Open to more choices on inverters, what do you own?.

Have a 24V system using a Samlex EVO 2224. It's been working, now I'm putting together a larger system that will have one Outback Radian 8kW and one Radian 4kW inverter. The 4kW should run most anything, and, given what I've been able to piece together of the design, no single failure should leave me with less than 8kW of inverter capacity. AIUI, the Radians use a control board and two 4kW power boards for the 8kW model, and I've seen reference to upgrading a 4kW to 8kW if you can source the power board.

One of the features the Radians (and some others) have is the ability to support an AC supply to maintain a steady load on the AC in supply and charging or drawing from the batteries to maintain your specified load, whether that's grid in or a generator.

RedNeckTek said:
LOL! Unless you live in the PNW, then you're screwed.

I've seen days with well under a quarter the sun production potential. That'll suck down a battery fast.
 
Have a 24V system using a Samlex EVO 2224. It's been working, now I'm putting together a larger system that will have one Outback Radian 8kW and one Radian 4kW inverter. The 4kW should run most anything, and, given what I've been able to piece together of the design, no single failure should leave me with less than 8kW of inverter capacity. AIUI, the Radians use a control board and two 4kW power boards for the 8kW model, and I've seen reference to upgrading a 4kW to 8kW if you can source the power board.

One of the features the Radians (and some others) have is the ability to support an AC supply to maintain a steady load on the AC in supply and charging or drawing from the batteries to maintain your specified load, whether that's grid in or a generator.



I've seen days with well under a quarter the sun production potential. That'll suck down a battery fast.
Samlex looks like a quality unit. If they only make them a little larger capacity. Seems like we have to go with Growatt or MPP to get higher capacities
 
If they only make them a little larger capacity.
How much capacity do you need?
 
8k with good surge headroom for my deep well and crawlspace sump pumps. I am concerned with the pumps and not any HVAC units. I have looked at the 4248 and like it.
 
8k with good surge headroom for my deep well and crawlspace sump pumps. I am concerned with the pumps and not any HVAC units. I have looked at the 4248 and like it.
I just read this
  • 3X surge power for high surge loads on start-up, such as compressor or refrigerator
  • Power overload allowances available for short periods of time. Overload allowances decrease with length of time. Increased inverter capacity, or “Active Power Boost,” means you can size your inverter smaller to handle heavy surge loads, reducing costs.
  • This unit may be all I need.
 
I just read this
  • 3X surge power for high surge loads on start-up, such as compressor or refrigerator
  • Power overload allowances available for short periods of time. Overload allowances decrease with length of time. Increased inverter capacity, or “Active Power Boost,” means you can size your inverter smaller to handle heavy surge loads, reducing costs.
  • This unit may be all I need and a big plus it's UL listed..
 
Samlex looks like a quality unit. If they only make them a little larger capacity. Seems like we have to go with Growatt or MPP to get higher capacities

Magnum Energy makes the MS4448PAE. It is 48VDC to split phase 120/240VAC Inverter/Charger and is stackable up to 4 units for 17.6kw. It can supply 8.8kw from 2 units with the required support equipment. Start out with one and add as needed. Magnum is a tier 1 supplier made in the USA.

Check out their web page https://www.magnum-dimensions.com/product-inverter/4400w-48vdc-pure-sine-inverter-charger-ms-pae


Magnum Energy makes the same inverter in a 24VDC model too, but for your power requirements 48VDC would be recommended system.
 