Make the scc fuse 80 amps to consolidate the bom and keep less spares.@smoothJoey Visual Diagram of your Ladder Drawing, how does it look?
Yes.
- On the positive coming out of the smartshunt to the 1A fuse on the fuse box, will I be running this wire from "VBatt +" output (green area) on the shunt?
It will be easier to land the small guage wire on the fuse_block.
- On the BatteryProtect, just curious on why I'm running it to the fuse box, isn't the negative bus bar a more direct path to ground? Does it matter?
But if you want to find a ring terminal to fit your negative busbar it will be fine.
What busbar are you using for the negative?
Yes.
- We talked earlier about putting a master switch on the battery circuit, does the 150A breaker serve as this master switch?
No the 15 amp fuse will blow but you still need a fuse at the fuse block.
- I know you fused for wire size. The 12V fridge has a 15A internal fuse. By fusing it at the fuse box, basically this means if overcurrent occurs it will blow the fuse at the fuse box and not the fuse in the fridge, making for easy fuse replacement correct? Doesn't this mean I need to use a 15A fuse instead? (fusing for the appliance, not wire size)
Stay with the 30 amp fuse at the fuse block.
The fuse protects the wire.
- On the same note, the manufacturer recommends a 10A fuse for the MaxxAir roof fan. Won't I want the fuse to blow just a bit above the appliance's max operating current instead of 20+A over with a 30A fuse?
If MaxxAir wants a 10 fuse then feel free to use a 10 fuse for that circuit.
If you will recall I said we could tweak the circuits off the fuse block
Yes.
- You're recommending buying my bus bars, MRBFs, 150A breaker, and my fuse block from waytek correct?
If its the same Bluesea busbar sure.
- Or can I get the breaker and the fuse block from amazon?
Any pure copper fine strand wire will do as long as the insulation is rated for at least 90C.
- Also, where's the cheapest 100% copper wire and quality rings terminals? I want quality in my components, but for the best price of course!
This is the good stuff..
Lets make the default branch circuit wire size 12 awg with a 20 amp fuse.
Please buy good fuses.
That means littelfuse or Bluesea.
As for ring terminals I just get them at the orange big box store.
Gardner bender have served me well.
I use a rachet crimper for ring terminals and a special ferrule crimper for up to 10 awg.
Unfortunately you will probably want to make 6 awg square crimps for the solar charge controller.
If it were me I would let the mechanical lug on the solar charge controller crimp the ferrule onto the 6 awg wires.
For the heavy guage wires use pure copper welding cable with insulation rated for 105C.
Buy quality lugs and a good crimper.