Growatt ground screw not doing anything

rloveless

New Member
Joined
Jan 11, 2023
Messages
58
Location
Utah
I have a growatt 3000 lvm 48p. It appears that my ground neutral bond screw is not doing anything. I believe if I remove the ground screw it should remove the ground neutral Bond. Also the bond between ground and neural is a weak bond (with resistance)

Here a link to a video showing the issue:

i am running my inverter with my battery connected only... no ac input.

I live in the United States and bought this unit from a US distributer (signature solar).

Is this a known issue? Is anyone else seen this behavior when you remove your ground screw? Is anyone else seen the weak ground neutral Bond when the screw is in place? Maybe i got a bad unit?

Thanks for any feedback.
 
Last edited:
Maybe that's the wrong ground screw.
I'm not sure where it's located in the 3000.
 
Maybe that's the wrong ground screw.
I'm not sure where it's located in the 3000.
It's got to be the right one. There is a picture of a screw and a ground symbol right next to it. Grow what also sent me a screenshot of its location. 20230314_111741.jpg
 
There are several "ground screws" on the various boards. Only one is the bonding screw.
But, if Growatt says that's the right one. Then , maybe it is. I would still verify that the connection you are reading isn't coming from the cord.
 
There are several "ground screws" on the various boards. Only one is the bonding screw.
But, if Growatt says that's the right one. Then , maybe it is. I would still verify that the connection you are reading isn't coming from the cord.
 
Okay I removed those cords completely and I'm still seeing the same behavior. I wonder if this is an issue with all the growatts of this model or just mine.
 
Not sure, as I have the 5000 models.
But, I don't remember anyone else commenting about it.
 
I would think you could just hardwire neutral to ground externally.
If never used with shore power, don't think there is a need for dynamic bonding.
 
you may be checking NG on the AC-input, should check on AC-Output with AC-IN disconnected
 
Not sure, as I have the 5000 models.
But, I don't remember anyone else commenting about it.
I sent growatt support the video. They just got back with me. Apparently this model doesn't have a ground neutral Bond. ?
 

Attachments

  • Screenshot_20230314_175419_Gmail.jpg
    Screenshot_20230314_175419_Gmail.jpg
    125.7 KB · Views: 15
I sent growatt support the video. They just got back with me. Apparently this model doesn't have a ground neutral Bond. ?
That would explain why I haven't seen any comments about it. Check voltage from L to ground.
 
I have a 3000TL LVM also and there was no G-N bond. On mine you need to jump the neutrals from AC In/Out in order to retain the bond from grid main service panel if that is your AC input source.
 