Just realized that they’re not the real problem, just how I was handling them. The way to avoid problems are some of the points noted in my last post. The real fix is to not connect the final wire until the switch is on and then using a resister to make the final attachment. And you can turn them on and off with no problems, just like with the inverter. I’m self taught, which means a hard and sometimes long learning curve!?I applaud you for continuing to use those switches even when multiple people are telling you they are wrong for your system.
You didn't look very hardDo you know what the torque is for SOK? On most of the equipment, I could never find this kind of information. ?
Sorry, I’ve been too busy trying to get my system up and running again. I don’t think the tightening of bolts is going to make that much difference.You didn't look very hard
The charge controllers parameters are set by VictronConnect app on my phone. I’m using the same settings for both batteries.Can you summarize the state of the system? I'm particularly interested to know how the solar charge controllers are networked with the shunt(s).
Both shunts are on the same network!You have two shunts. Which shunt are the solar charge controllers networked with?
I think because the VE Bus smart has has a temp probe built in, you have to add a temp prob to the start shunt for it to report back.Your screenshot shows three arrays but only one shunt. The Array #1 MPPT is using the current and voltage from the SOK shunt, but the temperature from the VE Bus Smart. That seems odd. Why isn't it picking up the temperature from the SOK shunt?
I think a screenshot from each of the three MPPT's networking screen would be helpful.
I'm going to throw out my theory here so anyone can pick it apart. The caveat here is that while I have a Victron shunt and use it in a network with two Victron MPPT devices and two 4s 280 Ah batteries, I haven't played around with the networking much
1. A shunt, by itself, does not limit charge or discharge
2. The shunts are reporting the voltage and current of each battery bank
3. Both batteries and shunts are attached to the same common bus bars
4. A solar charge controller that thinks it is charging the SOK battery bank, is also charging the Battleborn battery bank and vice-versa.
With regard to your question about fuses, I would be more concerned if you were using different types of fuses (Class T vs MRBF) or different brands.
There are two shunts, one off the SOK batteries and one off of the Battle Born Batteries. The Battle Born Batteries has the VE dongle that would report the temperature. SOK has none.Your screenshot shows three arrays but only one shunt. The Array #1 MPPT is using the current and voltage from the SOK shunt, but the temperature from the VE Bus Smart. That seems odd. Why isn't it picking up the temperature from the SOK shunt?
I think a screenshot from each of the three MPPT's networking screen would be helpful.
I'm going to throw out my theory here so anyone can pick it apart. The caveat here is that while I have a Victron shunt and use it in a network with two Victron MPPT devices and two 4s 280 Ah batteries, I haven't played around with the networking much
1. A shunt, by itself, does not limit charge or discharge
2. The shunts are reporting the voltage and current of each battery bank
3. Both batteries and shunts are attached to the same common bus bars
4. A solar charge controller that thinks it is charging the SOK battery bank, is also charging the Battleborn battery bank and vice-versa.
With regard to your question about fuses, I would be more concerned if you were using different types of fuses (Class T vs MRBF) or different brands.
Can you give me what the acronym of SCC is? ?I think because the VE Bus smart has has a temp probe built in, you have to add a temp prob to the start shunt for it to report back.
I do agree think changing any voltage setting on a smart shunt will just adjust the % readings and if linked to a SCC will report the voltage to the SCC vs the SCC terminal voltage as a controlling voltage.
A couple screen shots back you have current draw of both shunts reporting and the SOK was substantially lower.
I’ll try and change the fuse on the SOK batteries Sat, as it’s the first time I’ve tried this kind of fuse. That way I can find out whether it’s part of the problem or not. And I really don’t know if fuses have different resistance factors! ?