Careful if you ordered Apexium DIY Box (melted fuse cover)

MartyByrde

Off-Grid Innovator
Joined
May 16, 2022
Messages
151
Location
USA
IMG_7734.jpeg
 

Attachments

  • IMG_7736.jpeg
    IMG_7736.jpeg
    237.6 KB · Views: 116
  • IMG_7737.jpeg
    IMG_7737.jpeg
    187.6 KB · Views: 111
  • IMG_7738.jpeg
    IMG_7738.jpeg
    164.6 KB · Views: 108
  • IMG_7739.jpeg
    IMG_7739.jpeg
    125.7 KB · Views: 110
  • IMG_7740.jpeg
    IMG_7740.jpeg
    302.1 KB · Views: 118
  • IMG_7741.jpeg
    IMG_7741.jpeg
    234.4 KB · Views: 110
What was the load pulled from/to the batteries? And were they nuts torqued to spec?

The images shown heat, especially at the input side of the fuse holder. That only occurs if there is resistance, commonly caused by not properly torquing or bad crimps. In this case there are no crimps, so that can be ruled out.

I also seem to see a washer BETWEEN the busbar and the fuse. Thats #1 fail and will create heat for sure.
Nuts/washers are to secure the connection, NOT to be part of the conductive circuit


Imho it does more look like an installer/builder fault (they are DIY kits) and not a mfg risk/failure.

1707131850314.png

Was there anything mentioned about this in the manual how to assemble the pack? If not so they should include this.


Edit: It seems the same is the case between busbars and the front terminals. That also will heat up. Won't be surprised if the positive terminal (partially) has melted as well.
Can't see it clearly but it does look there is space there as well, indicating maybe a washer there?

Check all connections, also on the negative. There should NOT be any washers between conducting surfaces.

1707132218181.png
 
Last edited:
Unfortunately I see a lack of understanding of how to assemble high power electronics.
No washers in the current path, double check all connections including several days after running with load etc.
My battery kits wanted washers in the current path too but mine were copper/brass and I limited them to where absolutely necessary.
There were some height issues with the fuse holder/BMS and bus bars that need to be addressed. Or replace the fuse with a CB.
Also, looks like it may have got wet on the front panel and that + connector is toast.
 
Wow.
Several issues here...
Looks like the bms was bypassed...
Half the current path ignored, and a scary amount of power was being pulled.
I hope OP responds with photos and explanations of the build before failure...
 
Daisy is that you?

This box seems unsafe. Perhaps a cash grab, someone’s going to get hurt.
What was the load pulled from/to the batteries?
Difficult to say, when exactly this occurred. It seems like it was gradual over time. My system runs just during the day to maximize solar. The three batteries are there to smooth everything out. Between solar and battery it’s between 10 to 30 kW. I installed 224 panels from Santan used 250 W. But one day it just didn’t turn on and I noticed this.
IMG_7761.jpeg
And were they nuts torqued to spec?
Have you seen the manual?


It’s only pictures so I had trouble finding the torque specs. I did 60in-lb for the battery nuts.
The images shown heat, especially at the input side of the fuse holder.
I thought that would be tough to spot
That only occurs if there is resistance, commonly caused by not properly torquing or bad crimps. In this case there are no crimps, so that can be ruled out.

I also seem to see a washer BETWEEN the busbar and the fuse. Thats #1 fail and will create heat for sure.
Nuts/washers are to secure the connection, NOT to be part of the conductive circuit
Oh, I was just trying to follow the manual
Imho it does more look like an installer/builder fault (they are DIY kits) and not a mfg risk/failure.
can you clarify if you’ve seen the manual?

I’m learning every day and I welcome critiques, but your comments indicate you have not seen the manual. (Or you’re on the payroll like Ray says at the end of his build video.)
View attachment 193476

Was there anything mentioned about this in the manual how to assemble the pack? If not so they should include this.
did I misinterpret this photo:
IMG_7759.jpeg
I have two more of these battery packs, what needs to be changed on those?
Edit: It seems the same is the case between busbars and the front terminals. That also will heat up. Won't be surprised if the positive terminal (partially) has melted as well.
Can't see it clearly but it does look there is space there as well, indicating maybe a washer there?

Check all connections, also on the negative. There should NOT be any washers between conducting surfaces.

View attachment 193478
There are no washers here nor is this how it was. I loosened these intentionally when I took it apart because the pop on terminal was melted and I needed to use pliers to get it off. I didn’t want to bend this just in case.
IMG_7743.jpeg
The real question is how do I salvage this to get working tomorrow? Should I just skirt the 400A fuse and hook it straight to the BMS? Seems kind of pointless to have a 400 amp fuse on a 280Ah battery.
 

Attachments

  • IMG_7751.jpeg
    IMG_7751.jpeg
    291.4 KB · Views: 32
Wow.
Several issues here...
Looks like the bms was bypassed...
Half the current path ignored, and a scary amount of power was being pulled.
I hope OP responds with photos and explanations of the build before failure...
Can you clarify what you are talking about the BMS was bypassed? I built it following the manual. Did I miss something?
 
I'm thankful to see this. I haven't built yet, but was looking at that Apexium, and now I'm getting the benefit of learning more from others' mistakes. So thank you for posting this! I may not have made this mistake, but I might have, too, as I wasn't realizing the importance of keeping washers out of the current path.
 
I'm thankful to see this. I haven't built yet, but was looking at that Apexium, and now I'm getting the benefit of learning more from others' mistakes. So thank you for posting this! I may not have made this mistake, but I might have, too, as I wasn't realizing the importance of keeping washers out of the current path.
Yeah, be careful with the manual.
 
did I misinterpret this photo:
I think I would have followed that photo the same as you did. It does appear to have an in-current-path washer on each side of that connection, and I would have thought, looking at the photo, that the washer was suggested there to raise the bar above the level of the adjacent insulating material. Obviously, if the bar managed to pinch some of that insulation, it would not make a good connection. But that insulation may be just past the ends of the bar...I'm not sure how well the graphic portrays the actual setup.
 
Unfortunately I see a lack of understanding of how to assemble high power electronics.
No washers in the current path, double check all connections including several days after running with load etc.
My battery kits wanted washers in the current path too but mine were copper/brass and I limited them to where absolutely necessary.
There were some height issues with the fuse holder/BMS and bus bars that need to be addressed. Or replace the fuse with a CB.
Also, looks like it may have got wet on the front panel and that + connector is toast.
I’m learning and that’s something that if it’s shown in the manual, I’m going to duplicate it. Glad to know that now thank you.
 
I haven't seen the manual, I only made conclusions based on the images you've provided.

I agree the images you posted DO look there is a washer between the busbar and the fuse, which is wrong, unless they are 100% conductive like copper.

I'll check the manual (getting curious now) later this evening (its 3pm over here), since it seems there are mistakes in the manuals. I think Apex should improve/correct that off course since they will pose a high risk when pulling massive amps.

Can't blame for that since it seems to be wrong in the manual in the first place, which is only Apex to blame. If you're not familar with high currents, its not that uncommon to follow a manual (which is better than just doing something!)

And sorry for beeing too harsh, since you HAVE used the manual, only that one includes wrong information! Too bad you need to have this close call to find out.
 
1707142585383.png

Whether it's in the manual or not, this picture that was posted above needs to be addressed as well, the bus bar needs to go to the top of this copper bus bar, not the Zinc-Plated Steel PEM nut. I saw this when assembling my 3x Seplos cases and it's very easy to make this mistake.

I assembled 3x of the Seplos cases (which are exactly the same) and didn't have manual, so I haven't read it either.
 
I haven't seen the manual, I only made conclusions based on the images you've provided.

I agree the images you posted DO look there is a washer between the busbar and the fuse, which is wrong, unless they are 100% conductive like copper.

I'll check the manual (getting curious now) later this evening (its 3pm over here), since it seems there are mistakes in the manuals. I think Apex should improve/correct that off course since they will pose a high risk when pulling massive amps.

Can't blame for that since it seems to be wrong in the manual in the first place, which is only Apex to blame. If you're not familar with high currents, its not that uncommon to follow a manual (which is better than just doing something!)

And sorry for beeing too harsh, since you HAVE used the manual, only that one includes wrong information! Too bad you need to have this close call to find out.
Let us know if you see anything else if you do review the manual. I have two additional batteries and I want to fix. Which ones were you saying to remove?
IMG_7762.jpeg
 
Couldn't resist looking into the manual and I agree with the note from @Lt.Dan about the terminals.

The manual is, imho, wrong here. To me, the busbars should make direct contact to the terminals busbar, and the current should NOT be passing the (fixed) nut. That nut/thread is only to secure the bolt.

That busbar should be mounted exactly the other way, so the bar from the fuse makes direct contact with the busbar towards the terminals.

NOT as in this image where the supporting nut is part of the circuit.

1707143578004.png1707143726786.png

I found a picture in another Apexium thread:
This is how it should be in my opinion, not as in the manual

1707144127195.png

As for the washers: Remove washer C. So the fuse is in direct contact with the busbar. The washers on both sides should 'sandwich' the busbar/fuse, but not be in beween.

Current is passing the main circuit, busbar on busbar / terminal / fuse. Bolts/nuts/washers are to secure it in place. If there is no other way, use suitable conductive materials. Regular (steel/rvs) washers eg aren't.

When in doubt (And I personally always do on high current installs), run it for 15-30min and check with a flir camera. Any bad connection/resistance will show up very clearly.
 
Last edited:
Couldn't resist looking into the manual and I agree with @Lt.Dan note about the terminals.

The manual is, imho, wrong here. To me, the busbars should make direct contact to the terminals busbar, and the current should NOT be passing the (fixed) nut. That nut/thread is only to secure the bolt.

That busbar should be mounted exactly the other way, so the bar from the fuse makes direct contact with the busbar towards the terminals.

NOT as in this image where the supporting nut is part of the circuit.

View attachment 193505View attachment 193507


As for the washers: Remove washer C. So the fuse is in direct contact with the busbar. The washers on both sides should 'sandwich' the busbar/fuse, but not be in beween.
Yes, the fixed nut is called a PEM nut typically, made by PEM technologies. I used them daily at work. These ones are Zinc Plated Steel, and definitely NOT good for conductivity.
 
Which ones were you saying to remove?
I'm quite certain he means for the one labeled "C" in your image to be removed. You want the increased surface area of the contact between the bars, without the added resistance of the washer itself, which is not designed to be an especially good conductor.
 
View attachment 193501

Whether it's in the manual or not, this picture that was posted above needs to be addressed as well, the bus bar needs to go to the top of this copper bus bar, not the Zinc-Plated Steel PEM nut. I saw this when assembling my 3x Seplos cases and it's very easy to make this mistake.

I assembled 3x of the Seplos cases (which are exactly the same) and didn't have manual, so I haven't read it either.
So the female wire terminal was melted to the male. I had to snap it off with pliers and I didn’t want to risk bending this metal inside. Can you see this photo for how it looks tightened and if correct?

IMG_7766.jpeg

Docan’s engineer said I could remove the male plug and put a crimped 2/0 through the hole to attach to this busbar. With the 400A fuse being above the 250A battery disconnect I have installed, can I move all of the DK-1 busbar and connect it here:

IMG_7765.png
 
I think the busbar only has gotten very hot. Carefully clean, (very) gentle sand the contacts and if preferred renew heatshrink.

I would try replacing the fuseholder and positive terminals (You can buy them separate, if I remember correctly they are Futronics connectors), or you can replace them with 'regular' M8 pass-through connectors. ( https://www.aliexpress.us/item/1005005925179734.html for example)
 