What would be your recommendation for a decent 12V inverter in the 1,200W range (to power a sump pump) that has a low power consumption at idle?
Thanks
Thanks
What would trigger that switch though?I also wonder because of surge draw from the motor what size inverter you would actually need for this sump pump.
I would think any inverter with a “ECO” mode would be awaken by a sump pump. Eco modes have a real low idle, but need a certain amount of amps to wake it up; LEDs might not wake it up, but a sump pump would.
I use the Phoenix series of inverters by Victron. If you’re looking for a surge to 1200 watts, I’d recommend the Phoenix 1200 inverter. I have the 350 VA version and the idle load is quite low. If you’re looking to run at 1200 watts constantly, I would not recomend this.
Recommend looking through this thread:
Idle 'no load' Consumption: Specs vs Your Personal Observation
In this thread, I hope to consolidate personal observations/measurements on inverter standby consumption. Specifically whether your observations are inline with what is stated on the datasheet, along with anything else you consider relevant, interesting, good or bad. With time--if this thread...diysolarforum.com
Another option would be to wire any inverter that has a remote off switch to turn on through a sensor. This would draw less energy than any “ECO” mode.
I bet the sump pump already has a built in switch to turn on when the water floods to a certain level. If that’s the case, then wiring it would be more difficult.What would trigger that switch though?
What triggers the pump? I'll bet it's a level switch. Either repurpose that level switch or add a second.What would trigger that switch though?
Yes, but when the pump kicks in, the sensor will re-open quickly, and the pump will run on a timerWhat triggers the pump? I'll bet it's a level switch. Either repurpose that level switch or add a second.
Any idea why Giandel includes a 6 AWG set of wires? It's also the size they specify in their manual .....! I understand the math you provided, but if 2/0 is what I should use, it seems very weird the manufacturer talks about 6 AWGNo. I would use 2/0 from the battery to the inverter.
This is the ampacity chart I use:
View attachment 176098
The formaula I use from here is:
Amps=Inverter wattage / Low Voltage Cutoff / inverter Efficiency x 1.25
176 amps =1200/10/.85x1.25
I get 176 amps, so 2/0 with 75 Degree Celsius wire
When I put 12vdc, 120A and 3 feet, I get 4 AWGthis is what I look at when I want to know which wire size to use.
Nice file......thank you for creating it and sharing itAbout 6 pages into that thread that's already been posted I took all the results and put them in this spreadsheet for easier reading:
I don't know if anyone has updated it with further results since but when I bought a 2kw inverter it helped me pick the Giandel.Inverter Idle Powers
Inverters Dynamote,Brutus,120V,3,200W,88.0W,36 MPP Solar,lvx6048 (AIO),120/240V,6,000W,140.0W,No,42 EG4,3000ehv,12V,3,000W,68.9W,43 Growatt,SPF 3000TL LVM-24P,12V,120V,3,000W,58.0W,Yes,11.5W,51 Easun,Phoenix VE.Direct,24V,230V,1,000W,20W,18.4W,54 Exeltech,XP 1100-124,24V,120V,1,100W,20W,20.0W,5...docs.google.com
You could use relays to trigger the switch from the same device that triggers the sump pump. Put it on the same circuit with the timer that keeps the pump going.What would trigger that switch though?
Once the inverter's remote is activated by the sump pump switch......will it always stays ON?You could use relays to trigger the switch from the same device that triggers the sump pump. Put it on the same circuit with the timer that keeps the pump going.
What would be your recommendation for a decent 12V inverter in the 1,200W range (to power a sump pump) that has a low power consumption at idle?
Thanks
I am sure it depends on the inverter. Some just use a signal to turn on and when tha signal stops it turns off. That would be the easiest. If it took a pulse to turn on and another pulse to turn off, relays could do that too but it would be more complicated.Once the inverter's remote is activated by the sump pump switch......will it always stays ON
That tool/site looks at the distance which many amp rating charts do not. Having oversized conductors isn't a bad thing, it might cost a little more, and in some cases is preference. Thicker wire will run a little cooler even at short distances with constant amperage flowing.When I put 12vdc, 120A and 3 feet, I get 4 AWG
4 AWG is the recommendation up to 160A
For 165A, it shows 2 AWG
So...................2/0 seems huge. Am I missing something?