12V system review - temperatures, voltage drop

douglasheld

New Member
Joined
Oct 9, 2023
Messages
43
Location
London, United Kingdom
Hi all, I've recently set up a 2kW inverter with a single 130Ah battery and this is charged by a single 170W solar panel. The design purpose of my system is to allow occasional use of power tools or the shop-vac in my garage.

The original system I put together had poor quality cables bundled with the various equipment sets I bought on EBay. I evaluated with a thermal camera and decided that a number of improvements could be made.

I upgraded the inverter cables to 50mm^2 cables and learned to crimp the lugs. I've also added fusing, 2x2 MRBFs and an auto/marine fuse panel. The MPPT controller is now fused at 15A and I've upgraded the charger cables to 5.5mm^2.

I have a shop-vac rated 1700W which I use as my test of the system. With this running on AC power provided by the inverter for 6 minutes, I recorded how warm the connections got with a thermal camera. I also recorded a voltage drop of 44mV across the red cable, and about 55mV across the black cable (during the 135A test).

Notice, in the thermal photos, the thicker PVC insulated cables are still getting a little warm, while the copper lugs stay cold. I also notice the fuse holder busbar gets a little warm. I've snugged the nuts but not torqued them, due to the tall posts being longer than my deepest 14mm socket.

My requests are:
  1. Sanity check the measured power losses in this system.
  2. Sanity check the fuse sizes compared to ampacity of the cables.
  3. In particular, I recognize I've chosen the wrong cable size for the connection from battery to the fuse board. It has M5 screw terminals, and I think I can get lugs to fit up to 25mm cable. Is that a sensible size for that link?
Should I keep looking for problems to solve? Or does the system seem to be OK?

Cable / connectorDescriptionTemperature under 135A load / 6 minutes at 9˚C ambientUpgraded from
Battery terminalslead SAE terminal postsmaybe 14˚C-
Battery fusesdual MRBF holders on each + and -negative busbar gets 23Cno fuses
Fuse for inverter pathcube, 250A for each + and - paths20Cno fuses
inverter cables50mm^2 copper17-18˚C16.8mm^2 copper (2 x 8.4mm^2)
Fuse for fuse panel pathcube, 100A for each + and - pathsnot load testedno fuses
Cables to fuse panel5.5mm^2 coppernot load testednothing - no fuse panel
Charging circuit fuseblade fuse, 15Anot load testedno fuse
Charging cable5.5mm^2 coppernot load tested2.5mm^2 cable direct to MPPT charge controller
 

Attachments

  • v2 Front.png
    v2 Front.png
    2.3 MB · Views: 15
  • v2 right.png
    v2 right.png
    1.3 MB · Views: 4
  • negative MRBF busbar 23C.jpeg
    negative MRBF busbar 23C.jpeg
    19.4 KB · Views: 3
  • negative cable 16-18C.jpeg
    negative cable 16-18C.jpeg
    17.9 KB · Views: 1
  • inverter inputs and 50mm cables approx 16C.jpeg
    inverter inputs and 50mm cables approx 16C.jpeg
    65.6 KB · Views: 1
  • positive MRBF 20C. something 23Cjpeg.jpeg
    positive MRBF 20C. something 23Cjpeg.jpeg
    19.7 KB · Views: 1
  • overall system after test.jpeg
    overall system after test.jpeg
    18.5 KB · Views: 3
  • Electrical Panel v2.png
    Electrical Panel v2.png
    52.6 KB · Views: 4
Back
Top