Jeeze that seems much better than #3387v at 10a for 200' requires #12 gauge copper.
Voltage drop will be 1.93%.
Jeeze that seems much better than #3387v at 10a for 200' requires #12 gauge copper.
Voltage drop will be 1.93%.
CorrectThanks Everyone! That helps a lot! And if I was to add a second bank of panels in parallel with the original ones, I’d have the same voltage over the 10Ga wire, but at 20 amps?
Either is fine. But stranded is easy to pull through conduit.Also, when you say 10Ga, Solid or Stranded? I’m assuming stranded.
Not sure I follow?No way id run a single pair.
I mean, if i was running 200' of wire in conduit, i would run a spare pair for easy future expansion, or troubleshooting.Not sure I follow?
Yeah.. I just had to put in 270ft of two pairs of 10AWG but ran an extra 2 wires for a total of 6 wires just in case for future. Also included pull tape (since I had extra anyways) with the wires just in case that wasn't enough and needed to pull more.. As an extra extra backup ran a 2nd run of conduit since I never wanted to have to hand dig that amount of trench again!I mean, if i was running 200' of wire in conduit, i would run a spare pair for easy future expansion, or troubleshooting.
OK, I see. I always leave some poly draw string in my ducting, so easy to pull another pair later.I mean, if i was running 200' of wire in conduit, i would run a spare pair for easy future expansion, or troubleshooting.
Underground conduit rarely cooperates in that reguard.OK, I see. I always leave some poly draw string in my ducting, so easy to pull another pair later.
Well, I learnt something new today, thank youYou really aren't supposed to pull more conductors in a conduit with existing conductors. The moving conductors can rub through the insulation of the stationary conductors.
The correct way is to pull out the existing conductors and pull all in together.
Not sure skin effect would have any significance for AC at 50/60Hz at the wire diameters the OP would be consideringAt longer distances for AC the current is only flowing on the outsides of the wires (skin effect)
Actually, skin effect only is a factor at high frequency, or high voltage... 2500+V high voltage.Not at the distance, wire size or current.
I don't miss making those terminations. But the new cold shrink kits did make it a lot easier.