Unless I am very confused, the knockouts for AC lines in and out of a Sol-Ark 15K are 1.9", which is 1.5" nominal conduit size.
The Sol-Ark is rated for 4/0 aluminum or copper wire to handle 200A pass through from the grid.
But all the conduit fill charts and calculators I can find agree that even 3 4/0 wires are over the (US) NEC limit for 40% conduit fill, and I need 4 for L1, L2, N, G.
What am I reading or doing or thinking wrong? I am getting ready to install my 15K and making a detailed plan and parts list. I thought flexible/liquidtight vs EMT might be decided by the capacity calculations, but neither passes code that I can figure.
Thanks!