Same size as L1 and L2.thinking about what AWG the neutral needs to be, if considering a 240 load,
Noyou go with a much smaller AWG neutral than one would think.
Once you establish your grounding system (via the N/G bond). Everything connected to the grounding system is at 0v potential to the grounding system. Multiple connections to the earth are a problem for equipment. Because of the gradient pulse created by a nearby lightning strike.So this got me thinking about grounds and grounding rods/grounding potentials. I've heard it mentioned a debate about differences in potentials occurring in the earth at diff areas. So if it's recommended to run a rod at subs in separated buildings, and for ground mount arrays, how does the entire system know what reference potential to use. Is it an average of the potentials from all rods in the earth...or does it have to do with the G/N bond location...because it is closest to the rod at the Main Panel, this Main Panel Rod sets 0v reference, and all the other rods are more like relief valves but because of their distance from G/N bond/Main Panel Rod, they don't affect the authoritative 0v reference...just curious about that.
Current carrying conductor. When I was reading about derating for more than 3 in a raceway, someone mentioned that a neutral could not be a ccc in certain cases…still figuring that out.? CCC
YesI think I need a second #4 white leading back to the main from where the inverters are to cover the 60a circuit introduced by inv3&4.
Neutral is always a current carrying conductor.Current carrying conductor. When I was reading about derating for more than 3 in a raceway, someone mentioned that a neutral could not be a ccc in certain cases…still figuring that out.
Yeah...there are challenges/extra costs we have considered with putting it up by the service...I'd like to think this through before deciding how to proceed. We currently feel the best about keeping the equipment at the shop. Unless the complications exceed the alternative.You are definitely making it super complicated. By putting all of your equipment so far away from your service.
Balancing is good for the inverter. Doesn't change the conductor size.120v loads cancel on the neutral...maybe I could balance them to lessen the restriction.
YesCan you have a 100a double pole breaker, from the main panel, run through a 3 port polaris connector (for each leg) splitting to backfeeding one panel through a 40a double pole breaker, and a second panel backfeeding through a 40a breaker or higher breaker up to what the panel's bus bars can handle?
Additionally, let's say there is 2 AWG off the 100a into the polaris, then 8 awg from one port feeding the 40a breaker, and say 4 awg off the other port feeding the second panel lets say with a 60a breaker?
One of my outputs is 100ft, I guess it won't work.And the secondary taps (outputs from the Polaris) are no longer than 10'.
You would have to add a breaker within 10' of the tap.One of my outputs is 100ft, I guess it won't work.
That’s good…it was jamming me up. Here is the post in case you’d like to review.I'm not sure why they would say 2%. The industry standard is 3%.
But even at 5% there's no problem.
My design goal is always 3%.
I wouldn't be too concerned. The utility grid is only regulating to +/- 5%.That’s good…it was jamming me up. Here is the post in case you’d like to review.
Post in thread 'Grid wire ampacity calc. dist. to 6500ex's, 1 way or 2?'
https://diysolarforum.com/threads/g...-dist-to-6500exs-1-way-or-2.69725/post-881765