I've acquired a |48v|100ah|15s| lifepo4 battery and I want to add it in parallel to my existing |48v|100ah|16s| x 4 (400ah) array.
- The 15s battery has a recommended charge voltage of 54.75v and BMS over voltage cutoff of 56.25v
- Each 16s battery has a recommended charge voltage of 58.4v and BMS over voltage cutoff of 60v
I'm thinking of configuring a grid / solar charge cutoff of 55.5v for the entire array, so I would be consistently overcharging the 15s unit and undercharging the 16s units. This should produce a loss of about 5% (20ah) from the existing 400ah array (5ah per battery), but I would be gaining another 80ah in return from the 15s.
Is this doable without any long term issues for the 16s batteries? Are my estimates correct? I don't care about the long term health of the 15s battery by overcharging since I acquired it for very little.
- The 15s battery has a recommended charge voltage of 54.75v and BMS over voltage cutoff of 56.25v
- Each 16s battery has a recommended charge voltage of 58.4v and BMS over voltage cutoff of 60v
I'm thinking of configuring a grid / solar charge cutoff of 55.5v for the entire array, so I would be consistently overcharging the 15s unit and undercharging the 16s units. This should produce a loss of about 5% (20ah) from the existing 400ah array (5ah per battery), but I would be gaining another 80ah in return from the 15s.