3.65V *is* overcharged.
If you have a BMS trying to balance multiple cells, 3.4 or 3.45 volts is usually a good choice,
OK - I thought he was trying to do a top balance, which will be better a bit higher than 3.45, but not over 3.65V
3.65V *is* overcharged.
If you have a BMS trying to balance multiple cells, 3.4 or 3.45 volts is usually a good choice,
@SeaGal I am nominally doing a top balance.
I have about 0.25 V drop across the wires since finding some appropriate washers to clamp down on some wires.
Multimeter on the cell is reading 3.4 V with the PSU currently supplying 3.65 V at 5 A. If I drop the PSU to 3.45 V current drops off to 1.5 A.
Sounds like I'm done then?
Understood, but with the cells I have I don't have a choice, they're too tall for the rack case.I am not a fan of putting these cells sideways.
Creates a situation where the valve CAN leak.
Battery cells should point straight up...
I just redid my 4 big 200ahs.
Details in this thread with pictures:
https://diysolarforum.com/threads/d...nd-re-cabling-since-first-installation.77721/
Can the rack case stand so the cells are upright?Understood, but with the cells I have I don't have a choice, they're too tall for the rack case.
I can search for other cells but if I can get away with laying the EVE cells down that's best as I already have them.
That would mean that all the factory cells were on their side.Can the rack case stand so the cells are upright?
Alright, capacity test on the first pack is in! 102 Ah, 5.3 kWh. Looks like I really scored with this purchase!
One thing that is curious to me however is the discharge curve I'm seeing. All the cells were in lockstep voltage wise up through about 80 Ah of discharge, at which point the brand new 100 Ah Eve cell started falling behind the unknown 100 Ah cells in the pack, finally ending with that cell triggering the low voltage cutoff at 2.6V while the other cells were still around 3V.
I'd be interested to hear any thoughts anyone has, could it be that the unknown cells in this battery are just punching above their weight?
The BMS is off by a bit because it was reading a 3A discharge while the load tester was pulling 3.3A, I'll have to calibrate that in the future. The last picture is just starting to recharge.
I couldn't actually tell you. I assumed that the BMSs needed cal as I've seen a few posts about it. I don't trust my clamp meter down to readings that low so didn't verify past it being in the same ballpark.Which is more accurate, the BMS or the load tester?
I just fed my benchtop power supply through an RC wattmeter into the load tester. All aligned within a few milliamps, so the BMS calibration is off as I suspected.Which is more accurate, the BMS or the load tester?
What voltage did you finally top balance the cells to? Should be 0.1a at 3.55V then rest, and ALL cells need to reach this.Alright, capacity test on the first pack is in! 102 Ah, 5.3 kWh. Looks like I really scored with this purchase!
One thing that is curious to me however is the discharge curve I'm seeing. All the cells were in lockstep voltage wise up through about 80 Ah of discharge, at which point the brand new 100 Ah Eve cell started falling behind the unknown 100 Ah cells in the pack, finally ending with that cell triggering the low voltage cutoff at 2.6V while the other cells were still around 3V.
I'd be interested to hear any thoughts anyone has, could it be that the unknown cells in this battery are just punching above their weight?
The BMS is off by a bit because it was reading a 3A discharge while the load tester was pulling 3.3A, I'll have to calibrate that in the future. The last picture is just starting to recharge.
On initial charge before installing the BMS I took everything up to 3.6V each (the original 15s pack and the 1 new Eve cell) and then let it settle. Recharged with the BMS installed up to 56.5V, so 3.53/cell and let the BMS finish balancing down to 0 mA.What voltage did you finally top balance the cells to? Should be 0.1a at 3.55V then rest, and ALL cells need to reach this.
You can charge to 3.45, but you need to hold the amps down to 0.01a to achieve full charge.
3.65 also works, if the amps drop below 1A