AGS - Auto Generator Start Information Thread

AGS - Auto Generator Start Information Thread
The intent of this thread is to collect and share information to improve understanding of AGS systems, capabilities and limitations. This post will provide a starting point with the hope that others add, improve and correct any posted information. Hopefully this will help fill a need for accurate and helpful information on AGS.

Generators - meh
Fuel powered generators are seen by many to be everything from gross to just plain unnecessary. This is demonstrated by the relatively low traffic in the Fuel Backup Generator forum and also by Will’s hilarious (as in very fun to watch) disdain of a gas generator (see 02:54) when he had to buy one in order to test a battery charger. However, for some of us generators are part of our system and AGS vastly simplifies their use.

AGS: What is it?
AGS (Auto Generator Start) is a useful feature that provides the benefit of starting and stopping a generator automatically based on any number of conditions such as battery voltage, battery SOC, current draw, ambient temp, generator exercise, low oil level, over/under rpm, etc.

AGS: Why is it needed?
  • For many (most?) folks here AGS isn’t needed. It seems the majority of solar systems are grid-tied and are being built with plenty of solar and battery capacity to run several days w/out grid support. Also, many off-grid folks are located in places where solar irradiance is consistent enough to minimize or eliminate the need for a backup generator. Running a generator for these folks will be infrequent enough that the AGS is not a big benefit.
  • AGS is needed or helpful where a generator is often required to keep the batteries charged when solar yield isn’t adequate. Factors here can be: older solar systems where panels were undersized due to cost; locations with inconsistent or reduced solar irradiance; systems where humans won’t be available to manually start the generator, etc.
AGS may be helpful in the yellow or green parts of the map (and sometimes even in orange and red portions).
https://globalsolaratlas.info/map
View attachment 179421

AGS: Basic System Requirements
  • Generator:
    • Gasoline or propane generator with electric start and auto choke (the auto choke can be DIY to adapt a non-auto choke generator to AGS)​
    • Diesel generator with relays to warm the glow plugs/intake air heater, run the fuel pump, etc. (this will be triggered in the correct sequence by the AGS)​
  • AGS Trigger: A configurable component that allows the user to set conditions when the generator will start and stop. Components that sometimes have configurable AGS triggers include:
    • Inverter/charger
    • System aggregator like a Victron Cerbo or Outback Mate, etc.
    • Battery monitor
    • Sometimes the AGS module itself
  • AGS Trigger Types: Typically the AGS trigger is a simple dry-contact that opens or closes a circuit. That's it! All that expensive inverter/charger, etc. does is close or open a switch to trigger the AGS module. Other triggers include a 12 volt signal, e.g. Outback inverters. The AGS module will take the signal from the open or closed circuit (or the 12v signal) to begin a sequence of events that starts or stops the generator. This is where the magic starts to happen.
  • AGS module: The AGS module takes the simple signal from the AGS Trigger to replicate the steps typically initiated by a human to start or stop the generator. With the exception of standby generators, many (most?) generators sold in the US do not come with an AGS module. I’ve seen some generators advertised in AUS with AGS preinstalled and some as options in the US but for the most part assume this is an added part to the system. They coast roughly $250 - $500 USD with opportunities to spend more.
  • DIY AGS 'module': Assorted relays, timed relays, etc. can be combined to create a DIY AGS system at a lower cost than products available on the market. I hope to include links to well documented solutions in one of the posts below.

Example: AGS In Action
Components: Victron Cerbo GX (system aggregator) | Atkinson GSCM-P (AGS module) | Westinghouse Wgen7500DF (generator)
  • The Cerbo allows the user to set a number of start/stop conditions such as SOC, batt voltage, battery current, inverter temp, generator exercise, etc.
  • When a start condition is met the Cerbo closes a dry contact that activates the Atkinson AGS (Atkinson calls it a GSCM – generator start control module). The Atkinson AGS is programmed and wired to: a) close the on/off switch on the generator (this turns the generator on), wait a few seconds and then b) close the start/stop switch on the generator which starts the generator.
  • If the Atkinson AGS senses an AC signal from the generator it will do nothing until the Cerbo opens the dry contact at which point it will close the start/stop switch (turn the generator motor off) and open the on/off switch on the generator (turn the generator off) and then go into standby mode.
  • If the Atkinson AGS does not sense AC coming from the generator it will assume the generator is not running and will attempt three start sequences. (The Atkinson decision matrix and sequences are explained in great detail in the manual.)
  • An approximate wiring diagram is shown below.
View attachment 179429
I am using the Schneider XWPro, InsightHome, AGS, with a two-wire Generac. In the AGS, I want to set Generator settings --> "generator type" to "14", but cannot get it to change from "2". Any ideas?
----------------------
On-Grid
XW Pro 6848
MPPT 80-600 x2
InsightHome
Discover 42-48-6650 Li-Ion x3
Schneider AGS
Generac 6730 20KVA
230-W panels x24
 
I am using the Schneider XWPro, InsightHome, AGS, with a two-wire Generac. In the AGS, I want to set Generator settings --> "generator type" to "14", but cannot get it to change from "2". Any ideas?
----------------------
On-Grid
XW Pro 6848
MPPT 80-600 x2
InsightHome
Discover 42-48-6650 Li-Ion x3
Schneider AGS
Generac 6730 20KVA
230-W panels x24
The AGS mode needs to be in standby in order to change the gen type. Been there done that. Lol.

And just a note. If you go into the AGS menu and put mode into standby, your inverter will actually stay on, it will just put the AGS into standby. So you actually don't even need to have a power outage when you do this. :) (y)
 
The AGS mode needs to be in standby in order to change the gen type. Been there done that. Lol.

And just a note. If you go into the AGS menu and put mode into standby, your inverter will actually stay on, it will just put the AGS into standby. So you actually don't even need to have a power outage when you do this. :) (y)
Duh! My bad. I wonder if I will ever learn. Thanks!
 
Duh! My bad. I wonder if I will ever learn. Thanks!
There seems to be a whole family of settings that need standby, others not. A warning message would be nice, but this is Schneider--their whole GUI needs a major workover. The only way to tell is if you can't change the setting. Unfort, if you need to put XW in Stb, you have to go on bypass first, or a whole bunch of computers get mad.
 
There seems to be a whole family of settings that need standby, others not. A warning message would be nice, but this is Schneider--their whole GUI needs a major workover. The only way to tell is if you can't change the setting. Unfort, if you need to put XW in Stb, you have to go on bypass first, or a whole bunch of computers get mad.
The other thing is, they say if you don't cycle to standby then back into operating, after making settings, those settings could be lost if the inverter happens to lose DC power before it gets "mode cycled". (My goofy term for operating > standby > operating.)

Interesting though that the GUI is still basically exactly what it was back in the Xantrex days. But hey, it does work.... More can be said for the "working side" of the Schneider GUI than for some other brands of "newer" units... especially AIOs.
 
Is there a way to get auto start from an inverter (in my case Victron components) to work with an "electric start" type generator? In my case I have the Genmax 3500 and would like to set up auto start/stop. The generator has a push botton start as well as a small fob remove:

 
Yes, there are a number of ways to use the open/closed relay from the Victron inverter, Cerbo, etc.
1 - Checkout the Victron link in post #5 in this thread for their overview on what their devices offer and which may be best to use in your application.
2 - You'll need an AGS (home brew or purchased on the market) between the Victron device and the generator. I recommend starting with an e-mail or call to Atkinson Electronics (see post #2) to see if they have an AGS for Genmax generators. They list 350 applications but they don't include Genmax. They may have a current application that matches the Genmax requirements.
 