I have two 24V/3000/70 multiplus inverters vectron says to use a 300A fuse. I'm using 250A fuses and 2/0 wire so I could put a 300A fuse if nessisary. The 12V version uses 400A fuse and the 48V 125A so I feel 250A is sufficient for mine.
How big does the battery fuse need to be? Do you just add the inverter fuse ratings together? I also have a 30 amp, 8 amp and some smaller DC loads running off though battery. I'd like to leave 50 amps dedicated to that. I realized the inverters don't use more then 125A each.
2400/24 = 100 * 1.3 [130% (1/2 hr peak)] = 138.3 amps
138.3 * 2 = 43.6 [other DC loads] = 320
320 * 1.25 = 400 amp fuse with 4/0 wire
Or do I need a 500 or 600 amp fuse. ? Somehow it doesn't make sense that the battery fuse would be less than the sum of the inverter fuses. Thanks for your help.
How big does the battery fuse need to be? Do you just add the inverter fuse ratings together? I also have a 30 amp, 8 amp and some smaller DC loads running off though battery. I'd like to leave 50 amps dedicated to that. I realized the inverters don't use more then 125A each.
2400/24 = 100 * 1.3 [130% (1/2 hr peak)] = 138.3 amps
138.3 * 2 = 43.6 [other DC loads] = 320
320 * 1.25 = 400 amp fuse with 4/0 wire
Or do I need a 500 or 600 amp fuse. ? Somehow it doesn't make sense that the battery fuse would be less than the sum of the inverter fuses. Thanks for your help.