Blue Smart v Charge Controller

After you get all changes done - repost both and let’s make sure there are no other settings that need changed. Also, do you have a Smartshunt or BMV712? - if so post those settings too.
 
You have the charger settings set as a lead acid battery. The float is 13.8 - that’s too high for lithium (and the reason the charger was always working when the battery was full). Also, the temperature compensation needs set to zero. If you change the battery preset to Lithium- that should fix it - then change the absorbing to the 13.5-ish and float to 13.2v.
I've just gone out and changed it back to LiFePo4.

It's cost £6.15 since 8am and it's only 7pm now.
I've now set up a smart plug to turn it on two hours before sunrise and turn off at sunrise.

Unless I'm missing something, I would have thought they'd sell a gizmo that charged the batteries when they drain below a preset percentage.

I can't be the only one who would benefit from something like that.

Thanks for reply though.
Cheers
 
After you get all changes done - repost both and let’s make sure there are no other settings that need changed. Also, do you have a Smartshunt or BMV712? - if so post those settings too.
Sorry I've already changed it all back to LiFePo4 settings now.
Everything I have is in the photo.
(I was typing the post while you posted this)
Cheers
 
Updated photo containing all the things I've added over the weekend. Fuses etc.

1000010844.jpg
Cheers
 
While my system is much larger and 48 volts, I do have a similar situation.

My "Grid Charging" is coming from a Schneider inverter/charger I have it set to only charge to about 75% SoC. Then the Victron Smart MPPT is set to hit 95% SoC. As long as the PV solar power can keep the battery above 75 the inverter never goes into grid charge mode.

The other advice in this thread looks correct and should work well.

Set the MPPT for LiFePO4 with the absorb voltage at 13.8 volts. That will get the battery to at least 90% SoC and allow a little room for cell balancing. Hitting full charge with LFP can be tricky as it is common for one cell to hit the upper knee and run up too fast for the BMS balancer to catch it. Absolute 100% would be absorb to 14.6 volts, but you are most certainly going to have a cell run away long before you get there. 13.8 is 3.45 volts per cell and is still over 90% charged if it is allowed to absorb there for an hour.

The float voltage only has to be a little below this. I would think 13.5 is safe and it can stay there all day without stressing the cells.

As the others have said, be sure to set the temp coefficient to zero.

Now set the AC input charger so absorb at just 13.2 volts. That way, the solar does all the charging unless the battery falls below 13.2 or 3.3 volts per cell. And set the float voltage even lower. Anything over 12.8 is keeping the battery over 50% charged. Having your timer disable the AC charger is not a bad idea. I have "Time of Use" electric rates here. The rate doubles from 4 pm to 9 pm so I have my AC charging blocked during that time so it can't charge from grid at the high rate. Do you have a good idea how may watt hours you use in a day? Maybe set the AC charger to only put in that much energy, and only if the battery is low. With that 280 AH battery, you have 3.58 KWHs of battery storage. How much is used in a typical day?
 
While my system is much larger and 48 volts, I do have a similar situation.

My "Grid Charging" is coming from a Schneider inverter/charger I have it set to only charge to about 75% SoC. Then the Victron Smart MPPT is set to hit 95% SoC. As long as the PV solar power can keep the battery above 75 the inverter never goes into grid charge mode.

The other advice in this thread looks correct and should work well.

Set the MPPT for LiFePO4 with the absorb voltage at 13.8 volts. That will get the battery to at least 90% SoC and allow a little room for cell balancing. Hitting full charge with LFP can be tricky as it is common for one cell to hit the upper knee and run up too fast for the BMS balancer to catch it. Absolute 100% would be absorb to 14.6 volts, but you are most certainly going to have a cell run away long before you get there. 13.8 is 3.45 volts per cell and is still over 90% charged if it is allowed to absorb there for an hour.

The float voltage only has to be a little below this. I would think 13.5 is safe and it can stay there all day without stressing the cells.

As the others have said, be sure to set the temp coefficient to zero.

Now set the AC input charger so absorb at just 13.2 volts. That way, the solar does all the charging unless the battery falls below 13.2 or 3.3 volts per cell. And set the float voltage even lower. Anything over 12.8 is keeping the battery over 50% charged. Having your timer disable the AC charger is not a bad idea. I have "Time of Use" electric rates here. The rate doubles from 4 pm to 9 pm so I have my AC charging blocked during that time so it can't charge from grid at the high rate. Do you have a good idea how may watt hours you use in a day? Maybe set the AC charger to only put in that much energy, and only if the battery is low. With that 280 AH battery, you have 3.58 KWHs of battery storage. How much is used in a typical day?
Wow, thank you for taking the time to type all that.
There are two 280ah batteries in parallel and at present I've only had a TV and a monitor as loads. About 160 watts. There are a couple of usb things being regularly charged too but I assume they're relatively insignificant.
I'll make those changes in the morning and monitor it during the day.
Not the best weather for this kind of experimentation but then it rarely is here.
Many thanks
 
can I make it so that the CC takes priority?
In short, you can do so but it’s not easy or intuitive. Generally I do so manually by unplugging my blue smart charger when I don’t want it to be charging.

@Crowz recently posted their settings for their blue smart charger. Basically you tell the charger not to start charging until the battery voltage reaches a low enough point. I haven’t had the chance yet to try out his settings, but hope to this summer.

Edit: I believe what @Brucey suggests is a simpler method than what Crowz uses but I haven’t confirmed myself that it works as intended.
 
In short, you can do so but it’s not easy or intuitive. Generally I do so manually by unplugging my blue smart charger when I don’t want it to be charging.

@Crowz recently posted their settings for their blue smart charger. Basically you tell the charger not to start charging until the battery voltage reaches a low enough point. I haven’t had the chance yet to try out his settings, but hope to this summer.

Edit: I believe what @Brucey suggests is a simpler method than what Crowz uses but I haven’t confirmed myself that it works as intended.
By the time I've figured this out they'll have invented something specifically for it.
Interesting trying to do it though.
Cheers
 
I'll do as you suggest with the IP22
Make the changes to the preselected lithium settings, battery safe off, no temperature compensation, no equilisation .

Suggest 13.3 absorbtion charge, 13.2 float, this will charge the battery to around 60% SOC.
 
You can save that as a newly named preset so you can easily switch back and forth between settings

I’ve discovered that presets limit your options. Only in “user defined” mode can you access all the settings. How do you set things in user defined and save it as a preset? It doesn’t allow me to do so, but maybe I’m missing something.
 
By the time I've figured this out they'll have invented something specifically for it.
Interesting trying to do it though.
Cheers

I’m hoping for that, too! These Victron products are both more complex (lots of available settings) and more intuitive than what I was using before (renogy), if that makes any sense. Can be confusing until you get the hang of it.

You can also always use the Victron Connect demo library and make changes to the settings and post a screenshot here before making the real changes. People can reply and comment on your proposed settings, based upon what you’re wanting to happen.
 
I’ve discovered that presets limit your options. Only in “user defined” mode can you access all the settings. How do you set things in user defined and save it as a preset? It doesn’t allow me to do so, but maybe I’m missing something.
Should be able to click in the Battery preset section, under user defined, change the voltages etc then Create preset option should be available.

Screenshot_20240204_151427.jpgScreenshot_20240204_151438.jpg
 
I have my MultiPlus set to ignore the grid when the battery is above a certain charge, and I also have a timer on the grid input so it will only ever charge between sunset and about 3am. This way the batteries can get some charge if they really need it, but I also have capacity to store any solar power we make once the sun comes back up.

The grid connection never charges the batteries completely full unless I override the settings.
 
I didn't see a purpose for any preset other than user defined. Your programming it to do a job. Having different presets served no purpose for me since I was programming it to do a single job which is charging the batteries if the solar isn't able to. I don't want the charger doing anything unless something goes wrong (bad weather, etc) and the solar charge controller wasn't able to charge the batteries enough.

Thus 20something percent battery soc is where I want the ip22 to kick in. Otherwise I don't want it doing anything. So I just chose user defined and set how I wanted it to charge and when I wanted it to kick in charging. Then I clicked save and forgot it was out there unless discussing it on the forum :)
 
Having different presets served no purpose for me since I was programming it to do a single job

Yeah it took me a moment to figure that out 😜 You only need a single job. Since my application is a mobile one, I want the charger to do different things depending upon what I need at the moment. The user created presets are very handy for this.

Much kudos to you for figuring out how to set it to only come in when the solar isn’t enough. For those times when I have the grid available for long periods of time, I will use a preset using your settings to use solar first and only use the charger when the clouds are in for days on end (rare).
 
Thus 20something percent battery soc is where I want the ip22 to kick in. Otherwise I don't want it doing anything. So I just chose user defined and set how I wanted it to charge and when I wanted it to kick in charging. Then I clicked save and forgot it was out there unless discussing it on the forum :)
I would be more than happy if I could get it to behave this way.
Are you able to share your settings?
Sounds like a few people would benefit.
Cheers
 
Last edited:
Just to add to that previous post, the IP22 has now dropped down to around 160 watts.
Which is approximately what my TV etc is using.
Am I right in thinking that the batteries aren't being used for the load?
Screenshot of my smart plug attached to the IP22.
1000010872.png

Cheers
 
When it is first turned on or plugged in it will charge the battery slap full no matter what basically. After that it follows the programming.

Also after setting everything the way you want it you have to go into re-bulk voltage offset and click ok to accept the .1 again. If you dont do this part it will not work right.
 
When it is first turned on or plugged in it will charge the battery slap full no matter what basically. After that it follows the programming.

Also after setting everything the way you want it you have to go into re-bulk voltage offset and click ok to accept the .1 again. If you dont do this part it will not work right.
Ahh that clears that up. Thanks again
 