My system isn’t grid connected.What grid profiles are you using? I am using IEEE 1547 default 2015.
I have heard the California Rule 21 profile might be better for AC coupling when operating without the grid.
My system isn’t grid connected.What grid profiles are you using? I am using IEEE 1547 default 2015.
I have heard the California Rule 21 profile might be better for AC coupling when operating without the grid.
it's good if the panels are in the southern hemiAND... your panels are tilted North!![]()
This is likely a cause of the problems you have encountered. That profile does not support proportional freq-watt curtailment. The graph in https://diysolarforum.com/threads/b...oller-for-ac-coupled-solar.80666/post-1042422 shows large sudden battery current changes that are consistent with the micros only turning fully on and off.I am using IEEE 1547 default 2015.
The was my PV load shedder working. If I just turn off the "AC coupling" on my Schneider Inverters, this brute force on/off method is actually working fine. Maybe I should just consider the problem solved? The problem is that I was hoping that getting rid of the excess solar might help the AC Coupling work better so it could fine tune production to match consumption. I can run string 3 with AC coupling enabled. Unfortunately, it seems that once I turn on strings 1 and 2 production drops to zero and stays there until I hard boot the micro inverters. I personally don't have any type of frequency logger. It might be easier to solve this issue if I could see what was going on instead of just guessing. It appears that the Schneiders are causing the micro inverters to shut down. Turning off AC Coupling makes everything work, but if my load shedder glitches, I have no fail safe.The graph in https://diysolarforum.com/threads/b...oller-for-ac-coupled-solar.80666/post-1042422 shows large sudden battery current changes that are consistent with the micros only turning fully on and off.
You should try the default IEEE 1547 2018 profile.
CA Rule 21 profiles can also work but there are many different versions now, so it may take time to find the best for your system. The IEEE 1547 2018 default profile is newer superset. It would be best to get freq-watt working with SOC control for smoother operations. Frankly, with the appropriate SOC settings for freq-watt, your system should be able to handle large load turn off without significant issues (e.g. bat ovp) even without the PV shedding relays. BMS can typically handle 1X charging current for at least several seconds (enough time for freq-watt response) even when the SOC is high.I am going to try rule 21. I am also going to also try turning on the SOC control. I am happy with my voltage driven charging cycle, but maybe I can get SOC to work properly too.
Is it possible that the iQ8 are communicating with each other ? there is that 5-min grid integrity check upon turning on. Are the iQ8s shutting off within this 5-min or immediately ?The was my PV load shedder working. If I just turn off the "AC coupling" on my Schneider Inverters, this brute force on/off method is actually working fine.
I changed over to SOC control. My latest recharge cycle looks fine. It was cloudy here today, so I couldn't do much else.The IEEE 1547 2018 default profile is newer superset. It would be best to get freq-watt working with SOC control for smoother operations.
That seems odd. Perhaps there is another overall (i.e. not just for AC coupled charging) setting for max SOC charging limit?Once I had the strings staying on, I was surprised that they would charge all the way up to 100% even though I had set the Max AC Coupled value to 90%. I'm not sure the setting of the AC Coupled charging limit actually does anything. It appears that the frequency / watt function doesn't actually get triggered until the battery voltage exceeds the absorption volts.
Slow ramp up is another enhancement (along with others like like freq-watt and voltage/frequency ride-through) in the default 2018 profile based on newer standards. I doubt you had slow ramp up with default 2015 profile based on older standards that did not require slow ramp up. The slow ramp up and ride-through requirements were added to the newer standards after POCO's found that large number of home solar systems suddenly turning on and off actually made the grid less stable.I did notice that the ramp rate on the new profile is much more gradual. It takes about a minute for the panels to fully ramp up now (plus the 5 minutes before they even start to produce anything). It seemed like that ramp rate was removed from the old profile when Enphase did their firmware upgrade. So with the old profile everything turned on all at once. I don't think it used to do that.
Great progress! Good to hear the new grid profile and freq-watt working. Hopefully you can get the SOC based AC coupling figured out. It would be great if you could post your inverter settings at some point.So now I would say that I have the AC coupling fully working.
I will do that. I will also go through any information I have on how some settings seem to affect the operation of AC coupling.It would be great if you could post your inverter settings at some point.
I sure seem to remember that the IQ8 inverters were ramping up slowly before the recent firmware upgrade. Possibly, the ramp up had been over ridden in the firmware. A part of the firmware "fix", may have been to remove the override and respect the ramp rate (or lack of one) in the grid profile.I doubt you had slow ramp up with default 2015 profile based on older standards that did not require slow ramp up. The slow ramp up and ride-through requirements were added to the newer standards after POCO's found that large number of home solar systems suddenly turning on and off actually made the grid less stable.
Did you try the 200% setting on the iq8?My Settings:
Nothing Special here.
View attachment 206597
AC Coupling On
Recharge SOC 95 - Doesn't seem to make any difference
View attachment 206598
Battery Type - Custom
Charge Cycle - 2
SOC Control - Enabled works better with SOC
Battery Bank Capacity - 300 Ah
Maximum Charge Rate - 60% If the actual charge rate when AC coupling exceeds this, the inverters shut down. Hard reboot is then required.
Absorption Set Point - It appears that they will attempt to keep the voltage under this value when charging by using Frequency / Watts.
View attachment 206601
I need to know if there is a 200% / Hz profile that is IQ8 compatible. I found an "Off Grid" profile that is supposed to AC Couple with Schneider, but it says it is compatible with the IQ7 family only.Did you try the 200% setting on the iq8?
My Settings:
Nothing Special here.
View attachment 206597
AC Coupling On
Recharge SOC 95 - Doesn't seem to make any difference
View attachment 206598
Battery Type - Custom
Charge Cycle - 2
SOC Control - Enabled works better with SOC
Battery Bank Capacity - 300 Ah
Maximum Charge Rate - 60% If the actual charge rate when AC coupling exceeds this, the inverters shut down. Hard reboot is then required.
Absorption Set Point - It appears that they will attempt to keep the voltage under this value when charging by using Frequency / Watts.
View attachment 206601
I admire what you have done so far! I also had the same dilemma as you with Enphase + XW Pro and off-grid - sudden power demand drop/rise - the bane of an off-grid(er). I've decided to use the Enphase batts like one would a cap (albeit a massive one) in the simplest sense of the word. They have the power control & production-to-storage ratios tweaked quite well, especially with the IQ8s. Now that I was able to sleep comfortably with no imminent smoke in my future, I focused on solving the next challenge - AC coupling. Ideally I wanted the Enphase side to be in sync with the XW side, the way you sync a generator at a power plant before letting it output amperage to an existing grid. The Enphase micro-grid is my "grid" in this sense and the XW with its batts would be the power plant "generator" when supplying and a "pump" (like uphill hydro) when AC charging rack batts. (I also happen to have the Orient Power battsBack Ground
I have an Enphase system with 35*350 watt panels. It uses the IQ8+ micro inverters at 295 watts each. So the total possible output is 10,325 watts. The actual maximum output is about 9000 watts. I have 7 panels that face east and 28 that face west. The slope of my roof is about 40 degrees so I will never have both set of panels producing the maximum amount of power at the same time...
... Because of these issues manufactures make recommendations to limit the ratio of PV to inverter power, and PV to battery capacity. In some cases they even suggest that the maximum AC coupled PV be less than the DC coupled PV.
slightly OT; got a new LG heatpump dryer ~800-w 240vacFrankly, based on my testing, if I needed to run my dryer on a sunny day during a grid outage, I would be fine doing that as long as I waited till the batteries were full. I ran 4 loads of laundry today.