Doing more research, mosty harmless
The 4 MRBF should be mounted to the bus bars in your case if you have 4 batteries in parallel. This prevents melting the cable to 1 battery if you manage to drop a wrench across the posts there the BMS will hopefully shut it down. The other 3 will feed current through the bar down the cable to the shorted battery and melt the wire because it gets 6 times the current you size it for. A fuse at the bus bar would blow and that wire is safe.Actually I have 4 MRBF fuse holders, 1 for each battery. There is more surface for the fuse holder on the bus bar, therefor lower resistance connection. Prior to this forum I have never heard of mounting the fuse directly to the battery. Also haven't see it in 50 years of working with dc voltages. That doesn't mean it might not be a better way. The Bluesea 6006 switch is mounted directly to the bus which reduces connections and possible failure points. While maybe not the best the fuse holder, another MRBF, is connected to the switch protecting the down stream wiring to the inverter. Also kinda limits the ac output of the inverter to 30A. The ac side of the inverter will be hooked to a 30A breaker also.
Time to melt the insulation off the wire is 0.01 to 0.1 seconds when given that much current. Time to melt the wrench is 1.5 seconds. If you fuse directly at the battery the other 3 batteries don't care if the fuse blew on the shorted battery.
NOTE - Fuse curves for MRBF and Class T are basically the same when it comes to time to blow, 0.01 to 0.1 seconds. Mega is 0.5 to 1.5 seconds. ANL is 1 to 5 seconds. Choose wisely.