running the numbers for myself...
20mm x 2mm = 40mm^2
Al is about 60% the conductivity of Cu.
.6 * 40mm^2 = 24mm^2
3awg is 26.7mm^2, so it's pretty close.
Personally, if you have more of the aluminum, I'd double it up.
Aggressively scuff both sides with scotchbrite or sandpaper to remove oxide. Apply NO-OX-ID A-special to all contact faces. I would do the prep and NO-OX to even a single bar installation.
Aluminum is a good conductor especially when you factor in the price of copper. However, it's prone to surface oxides that reduce conductivity. Corrosion prevention is key.